Answer / prashant
As the losses of Transfomefer depend on VA characteristic
(copper loss on current & iron loss on current).So the
total loss depend on VA characteristic & power factor doses
not play any role.so rating are given in KVA not in KW.
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / raja
kVA is the unit for apparent power. Apparent power consists
of active and reactive power. Active power is the share of
the apparent power which transmits energy from the source
(generator) to the user. Reactive power is the share of the
apparent power which represents a useless oscillation of
energy from the source to the user and back again.
It occurs when on account of some inertia in the system
there is a phase shift between voltage and current. This
means that the current does not change polarity synchronous
with the voltage. But the heat generated in a winding as
well as the eddy current losses generated in a transformer
core depend on the current only regardless of whether it
aligns with the voltage or not.
Therefore the heat is always proportional to the square of
the current amplitude irrespective of the phase angle (the
shift between voltage and current). So a transformer has to
be rated (and selected) by apparent power.
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / bhavana
the losses of transformers are
1.iron loss
2.copper loss
the iron loss depends on the supply voltage & copper loss
depends on the current. but these two losses does not depend
on the phase angle between the voltage and current. hence
the ratings of transformer is expressed in terms of product
of voltage and current i.e VA rating. it is not expressed in
watts or KW. it is mostly expressed KVA.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ashok mishra
transformers are rated in kva not kv
ur question is wrong
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sethu
Transformer is give to primary voltage then output take to secondary supply, so transformer mension to kva.
Motor only take the power supply, so motor mension the kw
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bijendra chhetri
because transformer is not rated in kv is smalest and kw is
bigers ones.
Is This Answer Correct ? | 0 Yes | 24 No |
Do you know how to joint the H.T and L.T Cables?
23 Answers KESC, MGVCL, Nokia, Oil Country Tubular, Power Control, SAGT, Siemens, Simco, Vivek Engineers,
Explain how you intend to work under pressure to meet up with deadline target?
Hello Can I use step up HV transformer 440/4160V as a step down? Thanks Evgeny
What is inductance?
Why DG set rating in KVA
mostly the questions were from machines... d.c. machines, transformer, synchronous and induction all theory paper........ few from power system... but the level of paper was easy.....
Is there any specialised book to refer about fault level calculation both in MV and LV side??
We have one 500KVA transformer. We have tested REF relay and commissioned. After one and half year, due to some ground fault in one of the DB circuit Transformer tripped by REF relay. What will be cause and remedy. Please advise?
What happen if we give resistance to the armatuure of a dc motor?a
what is the disadvantages of common earthing for AC and DC equipment? (i am talking about inverter control room and inverter duty transformer earthing is common...?)
WHICH SUPPLY IS BETTER FOR 4 MW LOAD. 1)TO TAKE NEARER AVAILABLE 11 KV SUPPLY OR 2)TO TAKE 33 KV SUPPLY WHICH IS AVAILABLE AT 10 KM DISTANCE BY INVESTING NEARLY 50-60 LACKHS
which have higher efficiency transformer or induction moter