how can calibrate vacume trasmitter by HART COMMUNICATOR ?
Answers were Sorted based on User's Feedback
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. go to process parameter and change the follwing
parameters
LRV:760mmhg
URV:0mmhg
then press send .then cross check the transmitter with
master pressure calibrator
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / senthilkumar
for ex: the range is -760 to 0mmhg .
by following procedure we can calibrate the transmitter by
using hart
1.give the supply to transmitter
2: connect hart to transmitter with 250ohms series resistor
3.switch on the supply
4. hart shows device connected
5. LRV= (-)760 mmHG URV= 0 mmHG
6. apply pressure 760 mmHG to low pressure side and see the
output it will show 20mA.
| Is This Answer Correct ? | 2 Yes | 5 No |
Why flow/pressure transmitter before control valve?
re i got gre score of 950,and toefl of 69 is this score sufficient actually my husband is presently in US i need to go please help me
i have one absolute pressure transmitter for the range is -400mmhg to 400mmhg. If i do the zero trim at atmosphere the transmitter should be give 4ma or 12ma? which one is correct?
why dead weight tester called dead weight tester.
Which type of pressure can be measured by these elements?
How is plc installing done
what is the full form of psig.
Why 4-20 amps is being used in instruments? Why cant we use any other range instead of 4-20 amps? Why only 4 amps is taken as lower limit and why 20 amps is taken as the higher limit?
What is voltage regulator?
To become an Instrument DESIGN engineer, is there any softwares or training to become Instrument Design engineer, plz suggest me, Iam very much interested in designing.
What is the difference between DCS and SCADA?
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)