Answer / kashifraza
3-Core Cables:
These cables are used generally for a perfect balanced 3-phase system. When the currents on the 3-live wires of a 3-phase system are equal and at an exact 120° phase angle, then the system is said to be balanced. The 3-phase loads are identical in all respects with no need of a neutral conductor.
3.5-Core Cables:
A 3-phase system may have a neutral wire. This wire allows the 3-phase system to be used at higher voltages while it will still support lower voltage single phase loads.
It is not likely in such cases that the loads will be identical, so the neutral will carry the out-of-balance current of the system. The greater the degree of imbalance, the larger the neutral current.
4-Core Cables:
When there is severe out-of-balance conditions, the amount of fault current will raise to a very high level. Generally in the case of linear loads, the neutral only carries the current due to imbalance between the phases.
| Is This Answer Correct ? | 75 Yes | 6 No |
Answer / s.ravikumar
THE 3.5 CORE CABLE IS POWER CABLE (NORMALLY HIGH LOAD).
-3 LEADS WILL BE OF SAME SQ.MM
-1 LEADS WILL BE,HALF OF THE ABOVE 3 LEADS
THE 4 CORE CABLE CAN BE USED FOR BOTH POWER AND CONTROL CABLE(NORMALLY LESS LOAD)
-4 CORE WILL BE IN SAME SQ.MM
| Is This Answer Correct ? | 33 Yes | 8 No |
Answer / kapil tayade
3-Core Cables
These cables are used generally for a perfect balanced 3-phase system. When the currents on the 3-live wires of a 3-phase system are equal and at an exact 120° phase angle, then the system is said to be balanced. The 3-phase loads are identical in all respects with no need of a neutral conductor.
An important example of 3-phase load is electric motor and that is why, they are fed through 3-Core cables in most cases.
3.5-Core Cables
A 3-phase system may have a neutral wire. This wire allows the 3-phase system to be used at higher voltages while it will still support lower voltage single phase loads.
It is not likely in such cases that the loads will be identical, so the neutral will carry the out-of-balance current of the system. The greater the degree of imbalance, the larger the neutral current.
When there is some degree of unbalance and the amount of fault current is very small, then 3.5 core cables are used. In these types of cables, a neutral of reduced cross section as compared to the 3-main conductors is used, which is used to carry the small amount of unbalanced currents.
4-Core Cables
When there is severe out-of-balance conditions, the amount of fault current will raise to a very high level. Generally in the case of linear loads, the neutral only carries the current due to imbalance between the phases.
The non-linear loads such as switch-mode power supplies, computers, office equipment, lamp ballasts and transformers on low loads produce third order harmonic currents which are in the phase of all the supply phases.
These currents do not cancel at the star point of a three-phase system as do normal frequency currents, but add up, so that the neutral carries very heavy third harmonic currents.
| Is This Answer Correct ? | 20 Yes | 1 No |
Answer / ghulamsarwar3
3.5 MEANS 3CORE AND NEUTRAL IS HALF.4CORE MEANS ALL OF 4
CORE R SAME SIZE.GENERALY WE CAN GET 4CORE UP 25SQMM
CABLE,AFTER 25SQMM 3.5 CORE,NOW A DAYS 1,2,3,4,5,6,7,8
CORES ARE ALSO AVALBLE.
| Is This Answer Correct ? | 20 Yes | 10 No |
Answer / mukesh kumar
3 core is used for 3-ph loads/systems which do not require
neutral e.g. motors. 3.5/4 core is used wherever 1-ph
supply is also required (tapped between 1ph-N) in addition
to 3 phase supply. 4 core used for smaller cables usually
upto 16 sqmm where neutral core is of same size as phase
cores while 3.5 core is used for higher sizes where neutral
core is half the size of phase cores.
| Is This Answer Correct ? | 12 Yes | 10 No |
how capacitor pass ac voltage practically?with increase frequency and cpacitance?
what is the difference between UPS and INVERTER?
how is find out kwh step by step
why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.
hi i am aziz electrical associate engineer. i am faceing problem in acs800 vvvf drive.it is tripping wothout any alarm/fault.i cheaked all parameters and fault function of drive, all are correct as well as communication parameters.but still it is tripping (drive is tripping in running position not in starting)
Explain the advantages and disadvantages of hydropower plant?
what would happen if u assume to insulate all the overhead lines and no insulators....??do you think it to b an advantag or a disadvantage??justify.
what is the use of Turbocharger in a gen-set?
CBCT selection
what is the use of sdf?
In a star to star transformer can we use a common neutral for both star connected primary and secondary
The size and construction of bushings in a transformer depend upon?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)