What is full form of G.O.D in 11kv distribution?
Answers were Sorted based on User's Feedback
Answer / anantha murthy manja
It is Group Operating / Gang Operating Device. Both are correct.
Is This Answer Correct ? | 75 Yes | 15 No |
It's Gang Operated Device, It is a most commonly used switch in small to medium substations, Pole mounted Substations is a gang-operated, air-break disconnect switch.
The “Gang” refers to the three phases being electrically or mechanically tied together so that the 3 phases open at the same time. The “Air Break” refers to a visible break in the air that allows crews to see that the switch is truly open.
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / krunal jariwala
WHY WE NOT GIVE DC SUPPLY IN X'MER PRIMARY SIDE
Is This Answer Correct ? | 17 Yes | 17 No |
Answer / sandeep kumar badal
GOD stands for.....
G : Generator
O : Operator
D : Destroyer
Is This Answer Correct ? | 48 Yes | 54 No |
WHAT IS MEANT BY DERATING OF THYRISTOR?
When will you multiply and devide with derating factors to the actual value while sizing the cable?
Direction of flow of active power and reactive power with logic?
How to convert farad to kvar. both are the unit of capacitor.
5 Answers College School Exams Tests, UltraTech, Vikram Ispat Industries,
what is the difference between online & offline caliberation of KWH meters. Can Digital meters be caliberated
How to calculate the actual 3phase power, if the load current of each phase is not balanced
different aspects of voltage stability
what are balanced and unbalanced loads
What are the types of the glands and difference between single and double compression type of cable Glands.
0 Answers ABC, All Trades Electrical,
What is the difference between AC Drive and VFD?
what is the disadvantage of leading power factor...why can't we use it (pf=0) for a long period of time?
Why the motor take high starting current for long time(10- 15 sec) which is connected to Blower as compaire with a motor which is connected with pump with same rating?