we all know that in transformer, voltage and current are
inversely related i.e. Vp/Vs= Is/Ip....so in standard
CT..we have a ratio of 200/5...that means our voltage
should increase by ratio of 40..althoug that is not the
case...because that requires high insulation level.and
pratically not feasible......can anybody clarify my
ques.......thanx
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Voltage ratio is not applicable when the secondary of the Tr
is short circuited.Actually the secondary of CT has more
turns than the primary.No voltage is applied to primary of
CT and a small voltage is induced in secondary due to the
mmf created in primary by the current flowing through
it.When this emf of secondary is short circuited , the
current produced is proportional to the current in the
primary.That is why it is called CT and not just Tr.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / peter b
Current and voltage and still inversely related in a CT.
However, the primary of a CT does not see the full line
Voltage i.e. a CT on a 110kV bus does not have a primary
Voltage of 110kV! The CT's primary is in series with the
main load; the primary voltage of the CT is simply the
induced Voltage due to the AC flowing through the primary.
This Voltage is only a tiny fraction of the full line
Voltage. The only insulation requirement is that the CT as
a whole be insulated from neutral/earth. That's why they
are mounted on long insulators.
| Is This Answer Correct ? | 0 Yes | 0 No |
why in the three pin plug all 3 pins are cutted ?
how to select electronic timer(Star-Delta) setting for diff. rating motors
0 Answers Getrag Ford Transmissions,
When is lag lead compensator is required?
which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?
What is C curve and D curve of MCB?
what is the potential difference between line and earth?
how to generator maintenance (A Check, B check,Etc)
what is the functioning of cvt in a substation?
My switchgear busbar is rated at 2000A and just imagine the actual load on busbar is 1000A. From that busbar there are 10 outgoing feeders. Now the question is will the load be 1000A on each outgoing feeder or 100A per outgoing feeder. 2nd thing how do i calculate the load on individual feeder. Thanks for your time. Please provide some clarification on this issue.
what is the meaning of TPN
What is the formula formula for Busbar sizing and what are the things to be consider for Busbar Calculation?
how to determine the cable size...pls explain me with the formula taking particular load....does the factors like impedance & short circuit rating influence the cable size, if so how....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)