how to calculate temp.prapotional to mv in thermocoulpe.
Answers were Sorted based on User's Feedback
Answer / mohammad asfani
there is one formula with graphitical y=MX+b
for exma:Given a temperature transmitter with a measurement
range of -88 degrees to +145
degrees and a signal range of 4 to 20 milliamps, calculate
the proper signal output at an applied
temperature of +41 degrees.
Ans:take 41 deg and subtract to lrv mens -88. then 129 will
come and then you devide by span rang of transm..likespan
(145--88)=233,129/233=0.55 and take this number and
multiply by spanof current signal like 16ma and addto lrv
after that you can get ans...
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / mallu byali
Mohammad Asfani
as our Colleague said that is also right, but one more
simple way is that 1 mv is equal to 25 degree you can
calcutae bases on mv.nothing more
for ex 5 mv at element side then temp is 125 degree.
Is This Answer Correct ? | 1 Yes | 0 No |
How to Calibrate Ultrasonic flow Transmitter in Field
What is the potential contact / output??
1 Answers Vasava Engineering Private Limited,
what is sliding spool valves?
how to calculate flow range in DP tx
What do you need to consider when installing a flowmeter
How will you calibrate an interface level trol/normal level trol in line and in w/s?
why we use casced loop
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.
what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC
1 Answers Bharat Biotech, TATA,
What is the difference between Error and Offset.
what is vfd(variable frequency drive)?type of vfd.
How we can re-range the DP transmitter, range is -0.5 to 2.0bara. new range is -0.5 to 5 bar