HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD
EVEN AFTER IT IS DE ENERGISED
Answers were Sorted based on User's Feedback
Answer / dhandapani muthu.r, je tneb, i
Unless otherwise it is discharged and earthed it should be
treated as energised. We have to discharge and eath that
bus or cable with a set of earth rods. Then only it is
proved. We could also use a remote sensor to prove that it
is dead.
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / rod
As we are dealing with high voltage it is critical that the
correct procedure is used. 1/ A switching sheet should be
used to ensure that both sides of the test point is
isolated locked and tagged, 2/ A Modiwak (HV sensor) should
then be tested on a known live source first then the
isolated point should be tested and the Modiwak should then
be retested on the known live source, this ensures that the
Modiwak is functional, 3/ Then dressed in the correct PPE
earths may be installed, making sure the the earths are of
a size for the fault level at that point.
All the previous answers are partly correct but to prevent
accidents it is esential that a strict procedure is used.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / hassan
BOTH SIDES BREAKER OPENED , DE-ENERGIZED AND EARTH APPLIED.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / giri
Nowadays we have got HT sensors which will give indication
when it is brought near the live bus bar.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kedar
After taking all the necessary steps to discharge the bus-bars even then u r not confirmed. Then you should use a special meter which works on induction principle which senses the magnetic field of the bus bar and will tell u whether the bus is discharged or not.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / siddharth tayade
unless there is nothing any potential refrence to earth and
bus
Is This Answer Correct ? | 0 Yes | 3 No |
How to find the maximum load that can supply by a particular(say 315kva) KVA rated transformer?
while calculating demand in my company the present load in kw is 212.... there 125kvar capacitor bank is installed by spliting as 50 in departments...the diasplay in panek biard shows 175kw... how could we know the amount of kvar used to compensate the kva
What are the three major categories of error?
how can we know cable size for a given current? if any one have catalogue plz mail to vijay_raju369@yahoo.co.in
my N-P 230 VAC at 3 wires but i haven't any voltages at phase to phase whither my supply is 3 phase, why i haven't received these line to line voltages ?
I am having dual speed motor of cromton greaves make of 3.7 KW -1400 rpm and 5 KW - 900 rpm. Please let me know groups and winding connction for rewinding purpose.
How to calculate the sag on transmission Lines.
CBCT selection
what is bausbar?
Can any body describe me why a soft starter is used for 6.6kv induction motor instead of VFD ?
hello every one, what is the difference between the Kvar and farads, Rating on Power capacitor is for eg: x kvar, and normal capacitor is eg: x farads. what is the relation between these two?
where rlc series ckt used?