HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD
EVEN AFTER IT IS DE ENERGISED
Answers were Sorted based on User's Feedback
Answer / dhandapani muthu.r, je tneb, i
Unless otherwise it is discharged and earthed it should be
treated as energised. We have to discharge and eath that
bus or cable with a set of earth rods. Then only it is
proved. We could also use a remote sensor to prove that it
is dead.
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / rod
As we are dealing with high voltage it is critical that the
correct procedure is used. 1/ A switching sheet should be
used to ensure that both sides of the test point is
isolated locked and tagged, 2/ A Modiwak (HV sensor) should
then be tested on a known live source first then the
isolated point should be tested and the Modiwak should then
be retested on the known live source, this ensures that the
Modiwak is functional, 3/ Then dressed in the correct PPE
earths may be installed, making sure the the earths are of
a size for the fault level at that point.
All the previous answers are partly correct but to prevent
accidents it is esential that a strict procedure is used.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / hassan
BOTH SIDES BREAKER OPENED , DE-ENERGIZED AND EARTH APPLIED.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / giri
Nowadays we have got HT sensors which will give indication
when it is brought near the live bus bar.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kedar
After taking all the necessary steps to discharge the bus-bars even then u r not confirmed. Then you should use a special meter which works on induction principle which senses the magnetic field of the bus bar and will tell u whether the bus is discharged or not.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / siddharth tayade
unless there is nothing any potential refrence to earth and
bus
| Is This Answer Correct ? | 0 Yes | 3 No |
What are the protective devices in a DC/AC motor starter?
whether energy meter is connected in series or parallel.why?
15 suspects are rounded by the police and questioned about a bank robbery. Only one of them is guilty. The suspects are made to stand in a line and each person declares that the person next to him on his right is guilty. The rightmost person is not questioned. Which of the following possibilities are true? A. All the suspects are lying. B. The leftmost suspect is guilty. B only
What is A.C Resistance for Earthing ?
What is the minimum IR value of HT/ LT cable? Pls post separetely!!!!!
Why transformer rating is represent in KVA?
7 Answers Bhel, Sonalika, Usha Martin, Wipro,
In ups static switch if i gives the supply at output end it will open the circuit in stactic switch or not if it will open then how it operates.
Why we are measured insulation resistance applied through DC Voltage?
what is the procedure for erection of a transformer
will we get shock from dc?
what's the difference between abs/inc encoders. apart from the position remembrance what are all the other differences. and what's mean by grey code.
Where -48 volt DC use & why?????????
10 Answers Ericsson, INDUS, Indus Towers, Telecom,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)