Answer / ranganadh
Long distance communication mA signal is preferable than
mV, V signals to avoid noise. It cann't be predictable with
0 mA, whether the loop was broken or the signal itself. So
to avoid loop break problems we consider 4mA as the lowest
signal. Moreover, it is recommended to put a 250 ohms
resistor at the input terminals of the instrument to get
1VDC for 4mA and 5 VDC for the 20mA and further these
signals will be amplified by instrumentation amplifier in
the instrument circuit.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / jazz
4-20 mA signal differentiates live process 0% with 4mA
signal with a wire break (0 mA), current is also used for
transmission because even if your receiver or PLC/DCS card
is far away current signal sent proportionately by the
transmitter will be received as the same current at the
receiver/PLC/DCS card, although it is converted as a voltage
signal (1 to 5 VDC) by a 250ohm resistor, since
micro-processor process signals in voltage levels.
| Is This Answer Correct ? | 1 Yes | 0 No |
Why the tapping connections are taking above for gas service and below for liquid service?
How to work DCS? how to get the signal from Field Instruemtns to PIB to Console?
which types of oxygen analyzer describe with drawing ?
THE OUTPUT OF A CURRRENT TRANSMITTER OR A PNEUMATIC TRANSMITTER HAS A LIVE ZERO?EXPLAIN
What should be the main consideration while starting the Rotating compressor when we dont know the cut in and the cut off pressure setting of the pressure switch
what is diffrence between cascade & three element system.
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
how to calculate temp.prapotional to mv in thermocoulpe.
what is the PID controller?
3element
What is the difference between radar and ultrasonic level transmitter? Which method is best and more accurate?
What is Integral and Derivative control?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)