What is Procedure the procedure to select CT's & PT's in
66kV and above substation?
Answers were Sorted based on User's Feedback
Answer / rambabu
above is correct but the ct is current transformer for
measuring current and pt is measuring voltage in
sub-stations.these are using in HT sub stations only 1100v
and above.
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / kbonn
For example u have 100MVA transformer 66KV line
your CT ration 100,000,000/1.7320x66,000=874.77
so you can used CT ration 1000/1A
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / chandu
Current Transformers (CT’s) and Potential Transformers
(PT’s) are suitable located for supply to metering and
indicating instruments and relay circuits. CT’s are
connected at the terminals of each circuit breaker and PT’s
are connected right on the point where the line is terminated.
| Is This Answer Correct ? | 8 Yes | 11 No |
Why we are always only used 11 kv. , 22 kv ,33kv in transmission line? Why not use 25, 55 ,65 kv ?
3 Answers Khidmah LLC, Precision Camshafts Limited,
How to calculate the sag of OPGW during stringing???
what is general test conduted by transformer
why PT transformer primary r the grounded?
why we short ckt the secondry vo5tage/ winding in transfr and motor?
I HAVE A 50A MCCB AS PER DESIGN LINE WIRE CONNECT UPWORD SIDE AND LOAD IS CONNECTED TO DOWNWARD SIDE TO THE MCCB.IF NOW ANY ONE CHANGE SUPPLY & LOAD(WISEVERSA) WHAT HAPPENS ? DOES MCCB OPERATION OR WORKING FUNCTION NORMAL IF YES THAN WHY THERE ARE MARKED LINE & LOAD ON MCCB.
do we people experience any shock if we catch any one of the three phases (R Y B)in air with out touching ground.
A 2D array X(7,9) is stored linearly column wise in a computers memory.Each element requires 4 bytes for the storage of the value.If the first byte address of X(1,1) is 3000,what could be the last byte adress of X(5,8)?
WHAT IS VFD,FUNCTION, PURPOSE,
what solid earthing means?
How can I calculate the Mega watts required to run a plant having many electric motors and other electrical components.
What should be ideal IR value for 11kV, un earthed, 1 MW motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)