What is Procedure the procedure to select CT's & PT's in
66kV and above substation?
Answers were Sorted based on User's Feedback
Answer / rambabu
above is correct but the ct is current transformer for
measuring current and pt is measuring voltage in
sub-stations.these are using in HT sub stations only 1100v
and above.
Is This Answer Correct ? | 11 Yes | 6 No |
Answer / kbonn
For example u have 100MVA transformer 66KV line
your CT ration 100,000,000/1.7320x66,000=874.77
so you can used CT ration 1000/1A
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / chandu
Current Transformers (CT’s) and Potential Transformers
(PT’s) are suitable located for supply to metering and
indicating instruments and relay circuits. CT’s are
connected at the terminals of each circuit breaker and PT’s
are connected right on the point where the line is terminated.
Is This Answer Correct ? | 8 Yes | 11 No |
please write motor, transformer, Generator setting, fault level calculation of Tr.etc
pls give proper discription of selection of transformer based on particular load.
IN star -delta motors normally first operated in star mode {absulated given (r-y-b) phases after one miute change in delta mode in this case i am change phase sequience for example R -PHASE TO CHANGE Y-PHASE ;Y-PHASE TO CHANGE R-PHASE SO THIS TIME MOTOR WILL HAPPEN RUNNIG MODE EIGHTER(OR) STOP MODE(TRIP MODE)
In Transmission System if the potential difference at the two end of line are same then is the transmission of power will continue ? if yes then how.
what is power factor ?
specific gravity of a battery?
method to check earthing
why DC is not generated instead of AC?
what is electric current
What is the fullform of IPS in substaion using Aluminium Tubes
what will happen if a 3 phase motor is connected to a single phase circuit and vice versa?
Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of current?How can I calculate also when I have loads in KW?