Answer / samir rana
cu lossof x mer depends on current and iron
loss on voltage total x mer loss depends on va and not on
phase angle between v and i it it is independent of load
power factor. that is why rating og x mers is in kva and
noy in kw.
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / mustakul
iron loss depends on voltage and copper loss depends on
current.so transformer rating is in KVA not in Kw
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / praneetha
cu loss of a transformer depends on current and iron loss
on voltage.hence total transformerloss depends on volt
ampere and not on phaseangle between them.it is independent
of p.f.that is why transformers is in KVAand not in KW.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / nachu
Only the voltage (V) or Current (A) is stepped up or down and there is no change in the power (W). Power in this case is reactive power not active power so it is mentioned as KVA.
| Is This Answer Correct ? | 13 Yes | 13 No |
Answer / ahamadkutty
A transformer is rated in VA or kVA because the kVA is the
vector sum of Active power IR and Reactive power
IX(l-c)which a transformer can be delivered. So depending on
the connected load with active and reactive component the
power kW will be varied keeping the kVA maximm at the rated
kVA of the transformer.For a fixed voltage the current
supplied by the transformer is the maximum fixed by the
formula VA/V and maximum power by the load.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rahul rajpal
Transformer is not a load....That why it's rated in KVA
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / osman mehmetukaj
because to remain constant power transformer
while only changing currents and tension in the primary and
the secondary opposite, for example: Ip X Up =Is x Us =S
S(=)kVA
| Is This Answer Correct ? | 3 Yes | 7 No |
how to set earth fault relay
HOW DEFINE THE IP FOR ELECTRICAL EQUIPMENT AND WHAT IS THE IP OF PANELS USING IN HAZARDOUS AREA ?
why the blede and jow of isoletor demage in substation?explan.
What is the max demand on your transformer and your company?
10 Answers Bhel, CBRE, Core Consultants, HPL, IOCL, JLL, L&T, Lemon Tree, MNC, Rashmi, TATA, Tata Motors, Tata Power, Torrent Pharma,
How we can calc. the Backup time of a battery Bank???
Most electrical terms denoted by first letter of its name but Why current is denoted by "I".
what is negative,positive abd zero sequence current explain clearly
if we appling capacitor at above rated what are looses and what will be happen
4 Answers Radiant, Real Estate,
what happen if we give square wave instead of sine wave to the transformer
How to test transformer
What is the rating of a circuit breaker needed for 300 kv load in 33KV supply line of 33/415 transformer ? Whether 800/1200 amp vaccum circuit breaker can perform for a 33 KV line in input in 415 volt in output of the transformer ?
if u have to run a 300kw moter then what is ur choice HT or LT switchgear & explain why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)