The following equipment are installed ia a plant
1. 110KW Induction motor 4 Nos
2. 30 HP motor 3 Nos
3 15 HP Motor 3 Nos
4 7.5 HP motor 4 Nos
what is total load of plant if one of each is stand by.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
For electricty supplier, all are connected loads
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ankit kumar
the total load of plant is 112.94 hp if one of each is stand by.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / vinoth
For Electrical supplier all are connected loads so we shud
consider all the total loads.
1.110kw*4= 440
2.(30*0.75)=22.75*3=68.25
3.(15*0.75)=11.25*3=33.75
4.(7.5*0.75)=5.625*4=22.5
Therfore total in kw=564.5
Is This Answer Correct ? | 1 Yes | 2 No |
Explain different types of d.c motors? Give their applications
how to calculate of which rating transformer should be selected? take any example
We have given to 3phase supply to ups system & how can coming netural
what should be distance between two electrical earthing pit as per i.e.e
The series field winding has low resistance while the shunt field winding has high resistance. Why?
1.stranded resistance values of motors? 2.how to calculate the resistance values of single phase and 3phase motors?
In IDMT RELAY the term minimum (M) indicates what?
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
what is RMU ?
26 Answers MacLellan, Shalaka Infra Tech,
Which fault is caused by lightening and thuderstorm a. Line to line fault b. Single line to ground fault c. Double line to ground fault
how to select the cable size? any formula to calculate cable size?
What happen when ct secondary are open circuited? why same thing is not happen in ordinary transformer?