What should be cable size for 75KVA 380/220 3ph transformer
Answers were Sorted based on User's Feedback
Answer / shashi
P=1.732VI
SO P=75KVA(75000 VA)
V=220 V
I=236
Considering safety you can lay aluminum cable of 240 sqmm or 95 sqmm copper cable
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raja
4c x 50mm² Armoured Cable + 1c x 25mm² Earth Cable
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / essemmay
thanx raja..is it possible 50mm2 for both side cables..incomer and outgoing of the transformer, since the incomer voltage is 380 and outgoing is 220, so the same size is enough??
Is This Answer Correct ? | 0 Yes | 2 No |
what is STUB protection in tranmission system and switch yard area?
What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.
Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plant instrumentation field , which one field is give long life & which one field is best ,I confused a lot and also I'm studying AMIE, can I choose which department from Section B examination? pls tell me
what is the function of governor in dg set
1 Answers Igarashi, Medispray, Reddy Labs,
what is Anti-pumping?
what is charger supervision and control supervision?
How many types of DC current
hi friends can u tell me name of the sites where i can get animation of electrical machines......
In a poly phase circuit if clamp on meter shows same load on three phases and their sum on neutral then why we use three and a half core cable or maximum the same size of core as that of phase?
What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?
Whether power factor should be high or low? Why?
how to calculate the load on transformer..????