Answer / shashi

P=1.732VI
SO P=75KVA(75000 VA)
V=220 V
I=236
Considering safety you can lay aluminum cable of 240 sqmm or 95 sqmm copper cable

Is This Answer Correct ?    0 Yes 0 No

What should be cable size for 75KVA 380/220 3ph transformer..

Answer / raja

4c x 50mm² Armoured Cable + 1c x 25mm² Earth Cable

Is This Answer Correct ?    2 Yes 3 No

What should be cable size for 75KVA 380/220 3ph transformer..

Answer / essemmay

thanx raja..is it possible 50mm2 for both side cables..incomer and outgoing of the transformer, since the incomer voltage is 380 and outgoing is 220, so the same size is enough??

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is STUB protection in tranmission system and switch yard area?

9 Answers   KSEB, Power Grid,


What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.

0 Answers   AES,


Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plant instrumentation field , which one field is give long life & which one field is best ,I confused a lot and also I'm studying AMIE, can I choose which department from Section B examination? pls tell me

0 Answers  


what is the function of governor in dg set

1 Answers   Igarashi, Medispray, Reddy Labs,


what is Anti-pumping?

0 Answers  






what is charger supervision and control supervision?

0 Answers  


How many types of DC current

2 Answers  


hi friends can u tell me name of the sites where i can get animation of electrical machines......

1 Answers  


In a poly phase circuit if clamp on meter shows same load on three phases and their sum on neutral then why we use three and a half core cable or maximum the same size of core as that of phase?

1 Answers  


What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?

0 Answers  


Whether power factor should be high or low? Why?

0 Answers  


how to calculate the load on transformer..????

2 Answers   Bhel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)