I have 380.KVA DG set how to Calculate the units from DG.
Answers were Sorted based on User's Feedback
Answer / basavaraj
that depends upon the load p.f,with out considering the
load p.f 0.8, if we run DG for 1 hour it will generate
304kwh
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / azam
Physically You need 3 phase energy meter and 3 ct‘s to measure the units on hourly~monthly basis
By formula calculation is simple
power factor=kw/kva
KW=√3VIcosØ
| Is This Answer Correct ? | 0 Yes | 3 No |
which transfofrmer oil break down voltage strength get will be more if oil sample taken from bottom of tank or oil sample taken from top of the transfomer tank.
Define protection core in CTs Ex. 5P10, 5P20 etc.
What are the advantages of a three-phase system over a single-phase system?
define excitaton voltage and excitation current?
why transformer impedance measure in % (percentage)
In a ordinary plug can we hold the earth in hane and connect the circuit to supply?will we get a shock?
How LT megger works ?
WHY RATING OF VCB NOT LESS THAN 630A
What is RCBO? hw it works
if voltage is not builed up in small generator what will be the reason?
what will happen while giving 2 phase supply to 3 phase motor
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)