How will polarity test of Dy5 transformer ?
Answers were Sorted based on User's Feedback
Answer / arun r
VECTOR GROUP TEST [For 3Ф Transformer Only]
1. HV Side RФ & LV -1 r Ф Short Provide.
2. 3 Phase 4 Wire Supply Applied In HV
Side.
3. For Following Voltages Measured Are In
Volts
RY YB BR RN YN BN
ry yb Br rn yn bn
Rr Ry Rb Yr Yy Yb
Br By Bb Nr Ny Nb
Rn Yn Bn Nn
VECTOR GROUP = Dyn5
PROOF
1. Ry=Rb 3.Br<Bb
2.By<Bb
4.Yy=Yb
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / karthick
If I short Hv side Y phase and LV side r phase what will happen
Is This Answer Correct ? | 0 Yes | 1 No |
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
what is use of thermistor ?
What is Fan Coil Unit . How can we calculate CFM .
Explain working of PIU(Power Interface Unit) in Telecommunication,
7 Answers ACME, ATC, Bharti, HCL, INDUS, Pace Pharmaceuticals,
What is meant by turbo alternators?
what's the difference between abs/inc encoders. apart from the position remembrance what are all the other differences. and what's mean by grey code.
What are the difference between C-Curve and D-Curve for MCB's.
17 Answers ABB, DLF, Essar, GK companies, Nissi Engineering Solution,
what is a core company? why should we join a core company?
wHAT IS CAPACITANCE LATCHING? hOW TO CALCULATE CAPACITANCE LATCHING? hOW TO SOLVE THE PROBLEM IF CAPACITANCE LATCHING APPLIED?
how external lighting design? please give examples?
How to check the LM324 Ic
why name plate detail HP/KW rating of a motor is different from measured value HP/KW using formula?