1)what is hypo test. 2) which cable need to hypo test.3)
when hypo test can be done before or after glanding.4) what
is the purpose of hypo test.
Answer Posted / mukund
high potential test carried between line-line, line-
neurtal,line and neutral to graund on any control panelto
check insulation between live conductors and enclosure body
at hv like 1.5kv and onward depands on system voltage and
local standard, it is carried out also on control wiring too
e.g. from 300 to 600v it need 2.7kv test for 1 second and
2.4kv for 1 minuts,note when this test have to do test job
must disconnected from line voltage,it is most likely
megeer test, after testing it need to discharge tested line
to graund
| Is This Answer Correct ? | 37 Yes | 7 No |
Post New Answer View All Answers
From reading, Under voltage relay used also as phase sequence relay now, Why I use under voltage and phase sequence relay in the same circuit (ATS)?
technically, what is the reason behind starting the motor star the delta connection .. and what other ways to do this rather than using " star-delta transformer"
Why we use auxillary relay ? what is function of differential relay, directional o/c relay?
How test for Ddo vector group test condition?
What happens if the negative to earth voltage is greater than positive to earth voltage in the battery of substation?
Why a tesa lamp is glow between two phase?
sir pls tell me . our ct specifications are 120/5 ,2 core , 0.2 and 5p10 class , 30va and 30va buden. insted of 30 va i want use 15 va. can i use?
internally connection of photvoltic module
What are safety device in vcb and acb?
Why hydropower is called renewable source of energy?
Who are the manufactures those manufacturing 3Cx2.5sqmm FRLS cables. I heard about FRLS technology adopted only in wires useful for wirings
impliment (AB)`+C to transistor representation
Why earthing is necessary for any equipment?
Explain the functioning of diode?
whatare the disadvantages occur,if the form factor of transmission will not be equal to 1.11