There are two nos of 33Kv/11Kv 5MVA transformers conecting
through HT cable from substation having metering at
substation itself.One transformer used at a time another
remains stand by.Further 11 nos of 11Kv/440V transformers
are attached on it and each transformer is having its own
Power factor correction panel.Now one 33/11Kv transformer
at no load condition/Stand by condition is having power
factor in leading side upto 0.21 and while when another
tranformer at same situation have power factor in lagging
0.42. Now one thing is clear that transformer one is having
1.5 Km long 33kv cable due to that PF goes in leading side
and another is having only 250 mtr length remains him
lagging. Now i want to know that how i can maintain the
Power factor at no load/ stand by position though both are
behaving in seperate manner.
Answer / k.prakashchandra
Pf at no load is not to be heeded ,as the magnetizing
current is very low and the ct may not measure it accurately
wrt both magnitude and angle shift
| Is This Answer Correct ? | 4 Yes | 2 No |
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
what is soft starter? what is the difference between soft starter and star delta starter?
Give details on how you intend to handle a challenging position you are posted to manage unexpectedly as a company staff?
what is the min and max dc voltage for a dc system (110vdc)
Why rotating machines are not allowed to run near critical speed region?
What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side
How is efficiency of DG set calculated? At many places I found the efficiency to be mentioned in percentage. But at some other places I found kWH/ litres. I want to know how dimensionless percentage value is arrived at?
what types of electrical & mechanical test conducted in switchyard?
Why A.C. capacity given in Ton. Ex. - 1.5 Ton
what is floating charger and boosting charger?
define power quality
Is it reuired to use house service barcket for 31/2 core 300 Sq.mm cable,if the distance between pole & shop is around 2 mtrs only or can I hang the cable with GI support in air? upto what size of cable GI serrvice btacket is necessary?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)