How can you calculate in detail the VA burden of current
transformer used for Restricted earth fault protection?
Please understand that the CT required here is Class PX or
X. Also please show the calculations for knee point vtg,
stabilizing resistor, magnetising current.
Answer Posted / williamlobo
Restricted earth fault protection is a differential scheme,
with CTs on the transformer neutral and phase leads. The
phase CTs are connected together in parallel & then
paralleled with the neutral CT. The resticted earth fault
(REF) relay is connected across the paralled CT circuits.
The relay is either a voltage operated device (eg Alstom
MFAC14)or a current relay with an external setting resistor
(eg Alstom MCAG14). In either case, the scheme is set at a
voltage based on the maximum voltage that is developed at
the relay for an external fault. A practical setting is
50% of the CT knee point voltage, if full info is not
available.
| Is This Answer Correct ? | 3 Yes | 3 No |
Post New Answer View All Answers
describe the phenomena of vacuum interruption in C.B
what is Different between Bilinear and Unilenier?
What is the method of estamating of cable, CB,MCB ?
What is the classification of hydro projects based on installed capacity?
What is the power factor of a transformer at no load?
what is meant by poly phase induction motor ? how its operating by single phase or three phase?
wheather the size of windings in motor and generator are the same
how does high earth to neutral voltage affects electronic circuit?
What is difference and reason b/w -48V BTS system and 24 V BTS system. Plzzzzzzzzz tel me.
What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
Form S and "c" license application both are same? @ tneb portal
HOW TO CALCULATE THE REGULATION OF 100 AND 25 KVA TRANSFORMER
PLS SEND THE RRB CHENNAI MODEL QUESTION PAPER my email id is ganesan98655@rediffmail.com
can we make a electric generator,which can not use any type of fuel,air,solar,gas,thermal,coal,petrol,etc and able to produce electrical energy (or self electricity generating generator)