11/.433KV, 100KVA TRANSFORMER is supplied with .433KV AT
ITS PRIMARY. HOW MUCH KVA IT CAN SUPPLY
Answers were Sorted based on User's Feedback
Answer / vikramvijayk
Dear Mr.Nagaachi,
The answer is 100KVA(losses are negiable) because In an
transformer the KVA must be same to both side(PY&SY).
Is This Answer Correct ? | 10 Yes | 5 No |
Answer / vikas
As the xmer is havin its rating in kva so it depends only on voltage and current so if voltage increases thn current decreases and vice versa so if primary voltage is increased so its current decreases nd vice versa. So if secondary voltage is 11kv thn current in secondary will increase so i think kva will remain same.
Is This Answer Correct ? | 3 Yes | 0 No |
The full load secondary current of 11/0.433 kV, 100 kVA
trafo is 140 Amps. This much current only can flow on the
secondary. The secondary voltage when 433 V is fed to the
primary is 17 Volts (433x433/1000). Hence it would give
about 4 kVA. (1.732x17x140/1000)
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / hariharasudan cmrl
Transformers have step up and step down the voltage and never change the power
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagaachi
IT S ME WHO THE QUESTIAN IS ASKED,
MY IDEA IS THAT,
100KVA=ROOT3*11*5.2=ROOT3*.433*133
IF IT HOLD GOOD THE RELATION 5.2(root3*voltage)
thus we can get the answer as 5.2(root3*.433)=3.89KVA
PLEASE HELP ME GETTING THE SOLUTION
THIS QUESTIAN TEASING ME
Is This Answer Correct ? | 5 Yes | 6 No |
Answer / s.arul
Dear sir,
transformer only changed the voltage & current
rating. so not changed the KVA.
KVA = KV * A
SO, PRIMARY SIDE
100 = 11 * A
A = 100/11 SO CURRENT = 9.09 AMPS
SECONDRY SIDE
100 = .433* A
A = 100/.433 SO CURRENT = 230.95 AMPS
Is This Answer Correct ? | 3 Yes | 7 No |
How to test Alternator stability test for REF relay
What is the arc. I saw word arc in between sf6 & vcb brakers
how to find out three phase motr kw with out name plate..
What type of motor is used inside computer CPU.
What is the difference between security constraint unit commitment and security constraint optimal power flow?
0 Answers College School Exams Tests,
how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment
KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
what is cascade speed control device?and how this device control the speed of motors?
which VFD is better ( LT or HT)
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
What is the method to calculate the capacitor bank rating for say 50 KW load and how do we connect each capacitor to busbar??