11/.433KV, 100KVA TRANSFORMER is supplied with .433KV AT
ITS PRIMARY. HOW MUCH KVA IT CAN SUPPLY
Answers were Sorted based on User's Feedback
Answer / vikramvijayk
Dear Mr.Nagaachi,
The answer is 100KVA(losses are negiable) because In an
transformer the KVA must be same to both side(PY&SY).
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / vikas
As the xmer is havin its rating in kva so it depends only on voltage and current so if voltage increases thn current decreases and vice versa so if primary voltage is increased so its current decreases nd vice versa. So if secondary voltage is 11kv thn current in secondary will increase so i think kva will remain same.
| Is This Answer Correct ? | 3 Yes | 0 No |
The full load secondary current of 11/0.433 kV, 100 kVA
trafo is 140 Amps. This much current only can flow on the
secondary. The secondary voltage when 433 V is fed to the
primary is 17 Volts (433x433/1000). Hence it would give
about 4 kVA. (1.732x17x140/1000)
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / hariharasudan cmrl
Transformers have step up and step down the voltage and never change the power
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagaachi
IT S ME WHO THE QUESTIAN IS ASKED,
MY IDEA IS THAT,
100KVA=ROOT3*11*5.2=ROOT3*.433*133
IF IT HOLD GOOD THE RELATION 5.2(root3*voltage)
thus we can get the answer as 5.2(root3*.433)=3.89KVA
PLEASE HELP ME GETTING THE SOLUTION
THIS QUESTIAN TEASING ME
| Is This Answer Correct ? | 5 Yes | 6 No |
Answer / s.arul
Dear sir,
transformer only changed the voltage & current
rating. so not changed the KVA.
KVA = KV * A
SO, PRIMARY SIDE
100 = 11 * A
A = 100/11 SO CURRENT = 9.09 AMPS
SECONDRY SIDE
100 = .433* A
A = 100/.433 SO CURRENT = 230.95 AMPS
| Is This Answer Correct ? | 3 Yes | 7 No |
1kva = kw ?
how to calculate the ct burden?
If ROC does not lies inside unit circle,then ? a) Fourier transform converges b) Z transform converges c) Hatly transform converges d) Colpit Transform converges.
one 60KVA UPS how can full load current tell me us formulas
How many types are using in 220kv/400 kv swith yard
why 120 devided with pole and speed multiplication to determine frequency
as per standards how many neutral earthings and body earthings are needed.please help me
why ac supply neutral should earth not in dc (-)
What is PQA???Applications........
what does work of electrical technician in industrial
how to do 'pole drop test' on AC generator?
what is the generation action and motoring action?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)