11/.433KV, 100KVA TRANSFORMER is supplied with .433KV AT
ITS PRIMARY. HOW MUCH KVA IT CAN SUPPLY
Answers were Sorted based on User's Feedback
Answer / vikramvijayk
Dear Mr.Nagaachi,
The answer is 100KVA(losses are negiable) because In an
transformer the KVA must be same to both side(PY&SY).
| Is This Answer Correct ? | 10 Yes | 5 No |
Answer / vikas
As the xmer is havin its rating in kva so it depends only on voltage and current so if voltage increases thn current decreases and vice versa so if primary voltage is increased so its current decreases nd vice versa. So if secondary voltage is 11kv thn current in secondary will increase so i think kva will remain same.
| Is This Answer Correct ? | 3 Yes | 0 No |
The full load secondary current of 11/0.433 kV, 100 kVA
trafo is 140 Amps. This much current only can flow on the
secondary. The secondary voltage when 433 V is fed to the
primary is 17 Volts (433x433/1000). Hence it would give
about 4 kVA. (1.732x17x140/1000)
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / hariharasudan cmrl
Transformers have step up and step down the voltage and never change the power
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagaachi
IT S ME WHO THE QUESTIAN IS ASKED,
MY IDEA IS THAT,
100KVA=ROOT3*11*5.2=ROOT3*.433*133
IF IT HOLD GOOD THE RELATION 5.2(root3*voltage)
thus we can get the answer as 5.2(root3*.433)=3.89KVA
PLEASE HELP ME GETTING THE SOLUTION
THIS QUESTIAN TEASING ME
| Is This Answer Correct ? | 5 Yes | 6 No |
Answer / s.arul
Dear sir,
transformer only changed the voltage & current
rating. so not changed the KVA.
KVA = KV * A
SO, PRIMARY SIDE
100 = 11 * A
A = 100/11 SO CURRENT = 9.09 AMPS
SECONDRY SIDE
100 = .433* A
A = 100/.433 SO CURRENT = 230.95 AMPS
| Is This Answer Correct ? | 3 Yes | 7 No |
Give a brief idea about Control circuit wiring in Substation...???
where we use compound motors in real time and why?
whta is difference between contactor and breaker.
UG cable sizes were specified in sqmm. But practically its not coming to mesure. What's the reason for that? And how they specify the size of the cable?
What are the transformer losses?
motor and transformer working with same principle so why motor rotor was roted and transformer not roted
Why electrical heaters are not provided with overload relays in circuits
How to calculate 5hp 415v 3phase 2800rpm Ac motor full load current with out tourgh
WHY BREAKER ARE USED IN SUBSTATIONS?
what is the chemical name for oil that used in the transformer
Please clarify 1. Icw: rated short circuit working withstand capacity 2. Icu: Rated ultimate breaking capacity 3. Ics: Rated service short circut withstand capacity 4. other specification of ACB
what is the use of vcb & isolator in substation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)