what is the size of ht cable of 33kv ht line and
transformers ratings are 2.5mva and 5.5mva.please send
formula also.
Answer / eng. d
first, how will you install it?
underground direct buried, inside trenchs or above ground
any ways, the way to calculate will be done by the cable
vendor but you can do rough estimation
for 2.5 MVA transformer
= 2.5MVA/(1.73*33KV)=43 A
then cable shall be derated and much more than transformer
then we can say we select 60A cable rating
then we go to cable vendor catalog
try to see this
http://www.doncastercables.com/cableCalculator.asp
thank you
Is This Answer Correct ? | 10 Yes | 1 No |
How to calculate amount of copper used in a motor (AC&DC), generator and transformer? Datasheet provides power rating and mass of the equipment....can we somehow use this available info.
For Eg a 30 kw motor at full load how much kw it takes And at no load how much KW it will take?
What is the permissible value of earth resistance and as per which standard / act / rule ?
why nutral and earthing wire connect with each other in main panel board.?
what is the rating of power generation in india?
why some transformer without breather.
If a contactor need to replace with faulty one. what I want to check?
Difference between transition and diffusion capacitance
why 3phase is 440v but where as we get phase voltage 220v,we have to get 220*3=660v.can u pleas give in detailed
What is the importance of counter based plan & how is it scheduled?
What is the difference between PT for metering and PT for protection ?
WHAT IS A COLOUR CODING OF 3 CORE CABLE