Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the size of ht cable of 33kv ht line and
transformers ratings are 2.5mva and 5.5mva.please send
formula also.



what is the size of ht cable of 33kv ht line and transformers ratings are 2.5mva and 5.5mva.please ..

Answer / eng. d

first, how will you install it?
underground direct buried, inside trenchs or above ground

any ways, the way to calculate will be done by the cable
vendor but you can do rough estimation
for 2.5 MVA transformer
= 2.5MVA/(1.73*33KV)=43 A

then cable shall be derated and much more than transformer
then we can say we select 60A cable rating
then we go to cable vendor catalog
try to see this
http://www.doncastercables.com/cableCalculator.asp
thank you

Is This Answer Correct ?    10 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?

0 Answers  


What is the need for a controller?

0 Answers  


What are the effects of adding a zero to a system?

0 Answers  


Why are cables rated for 40 KA for 0.25 Sec fault current rating?

0 Answers  


HOW TO CALCULATE SINGLE PHASE AMPERES IN 3 PHASE TRANSFORMER? GIVE AN EXAMPLE PLZZZ

1 Answers  


what is the diffference between 3 point and 4 point starter ?

3 Answers  


Readings of ER300P Trivector meter

0 Answers  


Why can't we take NO LOAD TRIAL of motors having V1 mounting??

0 Answers  


How do we measure earth fault current in Generator Transformer(20/420kv),Station Transformer(20/11 kv) and Unit Transformers(20/11kv) for our plant system, since these don't have any Neutral earth Fault relay connected to their Neutral Earth? But for Unit Service transformers(11/.433 Kv) we have an Earth Fault Relay connected to its neutral earth.Why is such so?

1 Answers   NTPC,


i have 60Hz motor, can i run it at 50Hz power supply ???

2 Answers  


why we cant control neutral instead of phase in single phase?

3 Answers  


why reactor is connected before capacitor in APFC panel

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)