Answer / sunil ulange hit nidasohi
Sort circuit MVA= Rating * 100 / Z%
Short Circuit Current =Short circuit MVA / 1.732* Voltage
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / karuppannasamy
Rated primary current=2000/(1.732*33)=35A
Short circuit current= Rated current/Impedance
= 35/.075=466A
Similarly
Rated secondary current=2000/(1.732*11)=105A
Short circuit current=105/.075=1400A
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / madhu
Fault impedance in secondary Z = %Z x 10 x (KV)²/KVA
= 7.5*10*11*11/2000
= 4.5 OHMS
then fault current in sec = V/(Z*1.732)
= 11000/(4.5*1.732)
= 1411 A or 1.4kA
similarly in primary Z = 7.5*10*33*33/2000
= 40.83
then fault current in prim = 33000/(40.53*1.732)
= 0.466kA
Is This Answer Correct ? | 0 Yes | 3 No |
how capacitor buield up the voltage
What is meant by CFL & PL lamps
How to calculate the size of cables (all minium/copper) for a particular load
1 Answers BSL, Galaxy Power System,
Difference between transition and diffusion capacitance
How to convert 2 phase to 3 phase electricpower in induction moter?
Define Electrical Insulation and examples of Solid,Liquid and Gaseous insulating materials?
what is meant by brushed alternator & its working principle ?
On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?
6 Answers RR, TNEB Tamil Nadu Electricity Board,
Why 3 phase induction motor getting supply in body if one of it's phase is cut
how many percent setting of motor over load relay of its full load current
what is reactive power?
Meggering minimum acceptable Ohms for insulation resistance.