How to calculate the NGR value for a 2.7MVA Transfomer,
11KV system where the fault current has to be limited to
50A?
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited in your
case it is 50A.
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
| Is This Answer Correct ? | 6 Yes | 4 No |
What is the difference between newtral earthing and body earthing?
3 Answers JK Lakshmi Cement, NPCIL,
Is 3C x 2.5 Sqmm Cable can withstand 40Amp Starting current? If Yes then specify your ans.
in gen traf what is ONAN , ONAF , OFAF and DYN
how to check capacitor in general
What is Single Phasing fault???(not single-phase fault)
DIFFERANCE BETWEEN function of ELCB? function of rccb? function of mccb? function of acb? function of mcb?
What is the difference between IGBT and TRIAC?
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
Shall we get electrical shock if we touch the positive terminal of a 230 volt dc supply?
what is the meaning of osr in transformer.
what is load despatching
L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW MOTOR STARTS WITH EARTH FAULT RELEASE
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)