How many 2 ton window A/c can runs on a 125 KVA generator?
Answers were Sorted based on User's Feedback
Answer / hareesh k.s.
1 ton=1500W(App.)
2ton=3000W=3.75KVA
utility power of generator is 90%=125x90/100=112.5KVA
Therefore,no.of a/c's=112.5/3.75=33
| Is This Answer Correct ? | 39 Yes | 20 No |
Answer / sushovan das
1 Ton = 12000 Btu/hr.
also one Btu/h is equal to 0.293 watts so...One ton = 3.516
Kilowatts
Hence, 2 Ton = 2*3.516 KW = 7.032 KW
Let we take efficiency of Power Generator = 98%.
Hence, 125 KVA = 125*98% = 122.5 KW.
so no of AC can run on a 125 KVA Generator = 122.5/7.032 =
17 (nearest no) (Ans)
| Is This Answer Correct ? | 12 Yes | 12 No |
Answer / engr stev
Here is the answer with Simple Explanation...
Visit the link
http://www.electricaltechnology.org/2014/02/why-AC-rated-in-Tons-Not-in-kW-or-kVA.html
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / alex
You guys are close.
1ton does indeed = 1400 watts (starting power is higher than the continuous 1150 watts). But the power factor won't be 98%, it'll be more like 80%. So the 120kva = 100,000 watts.
2800 watts each works out to 35 or so 2ton window ACs.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / abhishek
1ton = 1400watts
so, approximately 38A/c can run on 125KVA generator.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / girish
50 A/cs of 2 Ton can run smoothly on a 125 KVA generator
| Is This Answer Correct ? | 9 Yes | 22 No |
how tto ingress mw in turbine explain.procedure ?
how to know the diffrential relay setting of 06mva step- down (delta-star)transformer?
types of motor starter
how to reduce the transformer size in ups ?
railway exam in asst loco pilot old test paper
25 Answers Indian Railways, Loco Pilot, RRB, Southern Railways, TATA, Vimal,
what is the method of electric earth for the protection of low voltage electric equipment
1 Answers MacLellan, Shiva Corporation, Siemens,
Why machine give shock
What is electrical earthing?
What happened if C.T mount at any cable or Bus bar in wrong direction . C.T going on proper work or not . C,T direction is essential thing to properly work.
How can you limit the fault level in a power system?
I know the Capacitor value- 12.5KVAR, voltage 440V gas filled, then what is the formula for calculate the microfarad value for this 12.5KVAR capacitor
In a Capacitor the electric charge is stored in:
2 Answers TELK Transformers And Electricals Kerala Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)