How many 2 ton window A/c can runs on a 125 KVA generator?
Answers were Sorted based on User's Feedback
Answer / hareesh k.s.
1 ton=1500W(App.)
2ton=3000W=3.75KVA
utility power of generator is 90%=125x90/100=112.5KVA
Therefore,no.of a/c's=112.5/3.75=33
| Is This Answer Correct ? | 39 Yes | 20 No |
Answer / sushovan das
1 Ton = 12000 Btu/hr.
also one Btu/h is equal to 0.293 watts so...One ton = 3.516
Kilowatts
Hence, 2 Ton = 2*3.516 KW = 7.032 KW
Let we take efficiency of Power Generator = 98%.
Hence, 125 KVA = 125*98% = 122.5 KW.
so no of AC can run on a 125 KVA Generator = 122.5/7.032 =
17 (nearest no) (Ans)
| Is This Answer Correct ? | 12 Yes | 12 No |
Answer / engr stev
Here is the answer with Simple Explanation...
Visit the link
http://www.electricaltechnology.org/2014/02/why-AC-rated-in-Tons-Not-in-kW-or-kVA.html
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / alex
You guys are close.
1ton does indeed = 1400 watts (starting power is higher than the continuous 1150 watts). But the power factor won't be 98%, it'll be more like 80%. So the 120kva = 100,000 watts.
2800 watts each works out to 35 or so 2ton window ACs.
| Is This Answer Correct ? | 4 Yes | 8 No |
Answer / abhishek
1ton = 1400watts
so, approximately 38A/c can run on 125KVA generator.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / girish
50 A/cs of 2 Ton can run smoothly on a 125 KVA generator
| Is This Answer Correct ? | 9 Yes | 22 No |
in short circuit. test of a transformer 5 to 10% ofvrated voltage is used why??? if we use rated voltafe then what will be?
what are the 4 rules to start the motor?
Can we use 11kv Trivector Metre or Energy metre instead 33kv Metre at 33kv Over Head Line metering purpose?
i m doing DEEE in part time,can i join regular cources in BE,,IF i join what the cources can i select like (civil,ece,IT) ,,kindly advice
what is ten delta test? what is the significanse of it
what is the working principle of electrical generator
what is the difference between megger and earth tester?
28 Answers Ashok Leyland, IOCL, RRL,
I try to check the three phase voltage in multimeter, in 125A isolator switch incommer. first i touch R phase, and then i touch Y phase using multimeter, the moment i touched, it blasts and that moment i got blindness. multimeter selector position is correct(750V AC MODE AND RED PROBE WASS IN v AND BLACK PROBE WASS IN COM. MODE. COULD ANYBODY GIVE ANSWER FOR THIS TO AVOID FURTHER ACCIDENTS PLEASE?
How we calculate DC inducation moter Amp? Sir pls give me formula......
Do these factors (settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot)) are the part of first order, second order, higher order, linear, non-linear, open-loop, closed-loop, homogeneous & non-homogeneous systems ?
Safety devices in SF6 Circuit Breaker?
HOW TO CALCULATE THE VT SIZING?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)