how to calibrate motorized operated valve?
Answer / subash krishnan
Instruments required:
Multimeter, potentiometer, point position trnasmitter (PPT), Valve Positioner, allen keys 3mm and 4 mm , double-end spanner (12-13), mini screw driver.
1.Initially check the motor-operated valve for open/close manually since the torque set should be accurate inorder for accurate calibration process.
2. Choose a potentiometer a desired based on the number of rounds in which the valve opens or closes. For example if the rounds are maximum choose a potentiometer which has the lowest resitance (1 kilo ohm).
3. Also choose the matching teeth wheel for the chosen potentiometer.
4. Take a point position transmitter (PPT) which is used to give the present position of the motor-operated valve. The PPT is of two different ranges based on resistance (0 to 230 ohms) & (0 to 500 ohms)
5. For every motor-operated valve the close position resistance is set as 100 ohms and the open position is set as 230 (to 500 ohms).
6. The point position transmitter is now given the power supply of 24V DC .
7. Now the resitance for the close position i.e. 100 ohms is given as input and the current should be tuned as 4mA.
8. Now the resitance for the open position i.e. 230 to 500 ohms is given as input and the current should be tuned as 20mA.
9. The steps 7 & 8 are repeated until the PPT gets set to 4 to 20mA.
10.Now the teeth wheel is matched with the matching wheel in the motor-operated valve setup so that the resistance could change in accordance with the valve's open/close operation.
11. The valve is now checked for open/close so that the current for open/close should be in the range of 4-20mA.
12. Now the positoner unit should checked whether it displays 0-100% for the open/close position. Otherwise the positioner display should be tuned for 0-100%
13. There is an actuator tuning adjustment in the positioner unit inorder to do fine calibration for zero and span if there are any minor errors in open/close position.
| Is This Answer Correct ? | 10 Yes | 0 No |
Where we cant instal mass flow meter.
What is the formula to convert mv to temperature in k type thermocouple?pls simply elaborate? I got one ans.it is Temp=mv×25°+atmospheric temp,but here what is 25°,i confusef ,so pls????
What is electronics?
how to calibrate the radar transmitter for measuring the exact tank level if tank is having agitator moving continiously because due to agitator tank surface level will vary every time.
why we set -10 volt in vibration sensor output,why not +10 volt
A RANGE OF TRANSMITTER IS (0-400)B mm abs what is "B"?
field bus transmitter calibration procedure tell me
how to calibrate the temprature transmitter MURCREYtype and thermocouple input type.
what is HVAC?
Why we use the remote seal transmitters
What is actuator what is motorized control valve?
why does mA signal preferred for signal transmission?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)