Determine the MVA rating of the power transformer given
that 110/66 kV,1000 Amps.
Folks how can i calculate the MVA rating with this Data??Plz
Help........
I have taken 66kv 1000A and pf as 0.85
MVA=MW/pf so firsrt we must calkulate MW
MW=(1.73*66*1000*0.85)/1000
=97MW
MVA=MW/pf
=97/0.85
=114 say 120MVA
There is no single transformer for 120MVA
so you can use 3*40MVA Transformers in parral operation
| Is This Answer Correct ? | 22 Yes | 2 No |
explain about RTCC
what is interpose vt where it is used and y it is used?
Why it need to form a capcitor when it not been in use from three or two year. Plz describe it technically.
Hoe to calculate body earthing conductor size ?
How do you commission a power Transformer?
what is the diff. between AVR & H.T.Stabilizer
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
What is ahu ? Working principal.
What is big transformer parts and their function ? Ty
ups battery design formula
why are we adopting 132kv,220kv for transmission rather than using 440kv at all transmission lines as it gives lower losses?
which part of transformer heats up the most and why? windings, core or oil .
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)