Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder
in LV substation panel.It is supplying to a lighting & power
socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8
times of Ir , tsd = 0.5 sec( I2 t off).
Sometimes this MCCB is tripping .But no trip in DB MCB.
Can anybody tell me reason ?
From where i can know about the MCCB settings?

Answers were Sorted based on User's Feedback



WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying ..

Answer / ranveer

Dear fren i think your Isd is very much high or it may
highest in. kindly che it out and may consult your vendor

Is This Answer Correct ?    4 Yes 1 No

WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying ..

Answer / mukesh khatri

check the terminationa and lugs

Is This Answer Correct ?    3 Yes 2 No

WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying ..

Answer / abdul

HI Friend,
I think there must be a earth leakage in your receiving end.
Always the MCB trips for Short circit,where as the MCCB
trips for both earth leakage & short circuit.

Is This Answer Correct ?    1 Yes 1 No

WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying ..

Answer / kyle

Hi,

Is it instantaneous tripping? If it is, Isd might be too low
(in fact it is consider high in this case) and tsd might be
too short, need to check the downstream loads.

might to provide more info?

Is This Answer Correct ?    0 Yes 0 No

WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying ..

Answer / naveen sahariya

This may be due to absense of discrimination feature in
DB.or cascading is not as per requirement.better to have a
word with siemens engineer

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

can transformer of different kvas be paralled

2 Answers  


What are the technical reasons for soaking transformers for various times before allowing them to pick load after a fault ?

4 Answers   GE,


Hai, I am from EEE branch.On feb 17 iam going to write an Exam for hindustan petrolium corporation Ltd.So plz send me the written exam pattern/Q's/interview questions.please mail to yuva_polisetti@yahoo.co.in

0 Answers  


A 11 KV motor is working. if the supplay is fail. what will happened with it's breaker? Trip / remain the same condition?

4 Answers  


what is deffrence between squirral cage and wound rotor in IM?

0 Answers   ME,


What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side

0 Answers   CEB,


What are the different pre-commissioning tests that are performed on the distribution transformer, power cable and switchgear (11kv)?

1 Answers   Hitech, Reliance,


what happens when we give supply to the secondary of a transformer ?? for example 415v(pri)/110v(sec)

2 Answers  


how to read AWG n how to convert AWG reading into mm?

1 Answers  


How to calculate the sag of OPGW during stringing???

0 Answers  


What makes the difference between 50Hz supply and 60Hz supply which one is economical? What is the use of using increased frequency?

5 Answers   ABB,


WHY IS HV WINDING OF A TRANSFRMER SECTIONALIZED???

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)