can we increase our frequency rate in INDIA?
Answers were Sorted based on User's Feedback
Answer / dharamveer
we can increase our frequency rate but on increasing f rate
our whole generation system has to modified which is too
much costly on other hand our appliance design has to
modified
Is This Answer Correct ? | 21 Yes | 0 No |
Answer / soumya
f=(n*p)/120;
f=frequency=50;
n=rpm=3000;
p=no of poles of generators=2;
changing p is quite impossible,
changing rpm is costly;
loads are to be changed;
so it is not likely to change f in any country
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / bhupendra & mayur
yes by coupling 50 hertz motor with the generator of 200 or
100 or required hertz so our input will be 50hertz with
output of required hertz(especially for testing purpose)
only.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashish mewada
WE can not increase frequency in particular system because
of in our power grid system equipment operate on 50 Hz also
in domestic industrial equipment working @5oHz.so it's not
harmful for this.
We can increase & decrease Frequency BY AC DRIVE IT IS
POSSIBLE
Is This Answer Correct ? | 1 Yes | 1 No |
why do we lay up the core of a cable?
How to calculate HV Cable Sizing & what are the factors to be considered for selection?.
Why earthing is required for diesel tank?
HOW WE CAN REDUCE THE CIRCUIT COMPLEX OF STAR-DELTA STARTER .BECAUSE NOW WE USING ONE TIMER RELAY & THREE CONTACTOR FOR MAIN,STAR & DELTA ?IF ANY IDEAS PLZ POST.THANK U
How do you select a cable size(Cu&Al) for a particular load
10 Answers Adhunik, BPCL Bharat Petroleum, Hiecon, TATA,
HOW DO YOU CAN CHECK A 15KV DIODE, WHETHER IT IS OK OR NOT?
CT Ratio of a energy meter connection is Red Phase : 100/5A, yello Phase : 50/5A & Blue phase : 100/5 A what is the overall Multiplication factor
What is the difference between the impedance percent and impedance voltage ?
What are the typical values of characteristic impedences of overhead line and underground cabel? Why there is so much variation?
What is servo motor and what are different types of servo motor
One Township having 850 house and each house load is 2.2KW single phase & 5HP 3 Phase motors of 10 Nos .Who can calculate 11 KV transformer capacity .dilip_bhasker@yahoo.co.in
If the kvar rating of capacitor bank is 600 kvar at 525V then what it's rating at 415v.