how to estimate the breaker capacity of breaker,please give
the one example( 6.6 kv breaker,800a)?????
Answers were Sorted based on User's Feedback
Answer / praveen
breaker capaciy taken by 132kv for example 133*1.55 times
capacity 145kv suitable for beaker
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / raghavendran.r
Step1: Calculate the system MVA.I have calculated that as 1.732*6600*800 = 9.144MVA. I have taken it as 10 MVA for easy calculations further.From the system MVA find out the Fault MVA value using the per unit impedance.i.e
Fault MVA = System MVA /P.u.Impedance.I am taking iot as .1
Hence we arrive at the Fault MVA.From this condition we get to know the Short circuit current as Isc = Fault MVA/Sys Voltage(6.6kV).
Usually, for a 6.6 kV system, the short circuit withstand rating is 40kA for 1 second.The Momentary current or making current is 2.55 times the Max. short circuit current.hHence we arrive at 100kA(Peak)
| Is This Answer Correct ? | 2 Yes | 2 No |
Fault current shall be part of tech specs of power cable or not?.
railway exam in asst loco pilot old test paper
25 Answers Indian Railways, Loco Pilot, RRB, Southern Railways, TATA, Vimal,
total numbers of earthing of a transformer
What is clean Earth System ?
what is the load amp of a 2 hp single phase motor?
if we have 380 KVA DG. how to calculate Power Factor. With detailed formula
I HAVE BEEN SELECTED FOR APGENCO A.E(ELECTRICAL) 2008.HOW MUCH WEIGHTAGE FOR INTERVIEW AND WRITTEN TEST.HOW I HAVE TO PREPARE. PLEASE GIVE INFORMATION IF U KNOW.WHAT ABT G.D THIS TIME.CALL RATIO 1:2
how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating using refference meter suppose we have 11kv/110v PT and 30/5A CT, the meter constant is 160imp/kwh, where meter is showing MW energy? give me solution which constant i feed in my refference meter for calibration of energy meter?
what is allowable current flows from phase to ground with out tripping the breaker
IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM
how can testing using megger?
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)