why the rating of transformer in only KVA not in others?
Answers were Sorted based on User's Feedback
Answer / naren
transformer having two kind losses .core losses and copper
losses . former depend on voltage while latter on current
so that why transformer rating is in KVA .
Is This Answer Correct ? | 14 Yes | 6 No |
Answer / ashwin
prakash i am fully satisfied with your nswer,as we have noidea of load on transformer.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vikram chandorkar
as we know that every electrical machine is having losses..transformer is having two kind of losses i.e core loss which generally depends on voltage and other is copper losses (i.e I2R losses)which depends on current.hence transformer rating is given in kVA
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / b.anil kumar
transformer is designed to supply full load current,that
means it is independent of load power factor.so it is in KVA
Is This Answer Correct ? | 1 Yes | 2 No |
1.Power factor of the load in not defined in case of
transformer, so it is not possible to rate transformer in KW.
2. The losses (Copper loss and current loss) of the
transformer depends on current and voltage not on load.
3. Transformer is not a load and having no effect on PF and
its only transfer the constant power from one voltage level
to another voltage level without changing frequency.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / khalid
because of transformer winding losses
winding loses are a reactive power reactive power is add
in active power so the rating of T.F in KVA
KVA = Apparent power
KVA =KW+KVAR
Apparent power =Active power+reactive Power
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / elango
the manufacturer does not know what type of load will be
used by user(it may be resistive ,capacitive , or
inductive) so it is all dependent on power factor. so only
it is rated in VA or KVA
Is This Answer Correct ? | 5 Yes | 7 No |
What is the estimated total hydropower potential of india?
how oltc works in rectiformers of higher rating (27 mva,200v dc,120kamps) please provide me full information with diaggram.
how do you reduce the skin effect
What is the Difference between Power Swing and Out of Step?
why a pilot exciter is used in combination with the main exciter? why not only a main exciter is used for excitation to an alternator?
what is real and reactive power?
A 12.5 hp slip ring motor taking high initial current and its MPCB is getting open.what may be the reason?
how to difference between the HT< cables
how to get electrical supervisor competency certificate in gujarat. i did 3 year diploma in electrical
Why we use series reactor in power system?
9 Answers Cadbury, HEG, Uttam,
why in scott connection of transformers, main transformer is tapped at 50% and teaser transformer at 86.6%?
5 Answers Bhel, Bosch, College School Exams Tests, Wipro,
We have 750KVA DG set, we want to introduce REF relay with 1250/1A,CL PS,Current transformers.The lead distance of 2.5mm copper flexible cable from CT to relay is around 5mtrs.We would like to know the knee point votage(VK) & IM calculion for CT's