why the rating of transformer in only KVA not in others?
Answers were Sorted based on User's Feedback
Answer / naren
transformer having two kind losses .core losses and copper
losses . former depend on voltage while latter on current
so that why transformer rating is in KVA .
| Is This Answer Correct ? | 14 Yes | 6 No |
Answer / ashwin
prakash i am fully satisfied with your nswer,as we have noidea of load on transformer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vikram chandorkar
as we know that every electrical machine is having losses..transformer is having two kind of losses i.e core loss which generally depends on voltage and other is copper losses (i.e I2R losses)which depends on current.hence transformer rating is given in kVA
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / b.anil kumar
transformer is designed to supply full load current,that
means it is independent of load power factor.so it is in KVA
| Is This Answer Correct ? | 1 Yes | 2 No |
1.Power factor of the load in not defined in case of
transformer, so it is not possible to rate transformer in KW.
2. The losses (Copper loss and current loss) of the
transformer depends on current and voltage not on load.
3. Transformer is not a load and having no effect on PF and
its only transfer the constant power from one voltage level
to another voltage level without changing frequency.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / khalid
because of transformer winding losses
winding loses are a reactive power reactive power is add
in active power so the rating of T.F in KVA
KVA = Apparent power
KVA =KW+KVAR
Apparent power =Active power+reactive Power
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / elango
the manufacturer does not know what type of load will be
used by user(it may be resistive ,capacitive , or
inductive) so it is all dependent on power factor. so only
it is rated in VA or KVA
| Is This Answer Correct ? | 5 Yes | 7 No |
how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating using refference meter suppose we have 11kv/110v PT and 30/5A CT, the meter constant is 160imp/kwh, where meter is showing MW energy? give me solution which constant i feed in my refference meter for calibration of energy meter?
why genarator genarating voltage 11 KV?
HOW TO CALCULATE AMPs OF CURRENT TRANSFORMER IN HT Panel
I have 2 KW electric water heater.I am gonna use it in controlling water temp.so I needed to increase or decrease the heating capacity.is there any electrical-electronic circuit for varying the resistance & so current?
how to make an earthing certificate
one 60KVA UPS how can full load current tell me us formulas
Whether earthmat designning is done only for sub station or it can be done for multy residential complexes also? What is the size, type & arrangement of the earth grid to be done?
What is difference between earth leakage relay and restricted earth fault relay ?
what is lumped and distributed elements?
what is the meaning of stub protection?
how set earth fault over current in relay
where does 22kv line starts
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)