one 60KVA UPS how can full load current tell me us formulas
Answer / rgs
GENERALLY TRANSFORMERS& GENERATORS ARE SUPPLIED WITH KVA
RATING AS LOAD POWER FACTOR IS NOT KNOWN.
kW = kva x pf
Prsently assuming rated voltage to be 415 v
A = 60 x 1000 / 415 = 144.
| Is This Answer Correct ? | 6 Yes | 0 No |
What are the Safety measures in central chiller plant? Explain them?
22 Answers Carrier, CPIC, HSL, JLL,
how much amp MCB is required for 1/2 kva power back up?
which type of winding is used for high voltage & low current?
What are the tests to be taken on a transformer and generator?
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?
deisel generators all elcetical calculation formule's
in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv, it operate or not???
role of europe union in UK safety legistlation (electrical safety)
why motor starting current is High ?
What is the difference between vector surge relay (78) and Pole slip relay (98G)
where we use the SFU & FSU?
in industrial lighting in each circuit how many lamps can be given? and how much load can be put on each circuit? is there standard for this? please help me with the standard description?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)