what will be the effect if we increase the excitation of a
alternator??
Answers were Sorted based on User's Feedback
Answer / jakeer
The output voltage will be high & due to this over voltage
relay will trip the Alternator.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / raul
If the excitation of an alternator is increased, then the
excitation voltage will increase, more flux in the air gap,
more rotor heating. But the excitation increase is governed
by the ROTOR HEATING LIMIT as per the generator capability
curve which over-rides the STATOR HEATING LIMIT. Above the
RHL, the automatic voltage regulator (AVR) takes over
control and starts reducing the excitation by Rotor current
limiter which acts in conjunction with the AVR.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is meant by inverse definite mean time (IDMT)& definitemean time (DMT)?
If a earth leakage circuit breaker trips is it possible to tell which house circuit breaker (I have four) is the faulty circuit?
If two generator running parallel, at that condition both ngr Taken in line or taken any one ngr, but why any one or both Ngr in line? Ngr is use for which purpose?
( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq
What are HT & LT Cables? What are their values?
Why do we perform an open-circuit test and short-circuit test on the transformer?
which motor is used in high mast ( street light) & give the hight of tower .
2 Answers Construction, Honda,
what diff. between earth nd neutral?
if there is a voltage difference between neutral and earth when we operate any instrument for fraction of time then where is problem?
Why an ac solenoid valve attract the plunger even though we interchanges the terminal? Will the poles changes?
how to improve my communication skills
7 Answers Infosys, MAHINDRA, Wipro,
suppose we using 3 phase motor of 440 v means what range of C.T. is require for measuring current ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)