what's transient & sub- transient reactance means?
Answers were Sorted based on User's Feedback
Answer / steven karris
These terms appear in the calculation of fault currents.
Common sources of fault currents are rotating machines,
i.e., motors and generators. An important factor in
detrmining the magnitude of a fault current is a variable
reactance that changes rapidly after the initiation of the
fault until it reaches a steady state.
Subtransient Reactance, usually denoted as X''d (X double
prime sub d), is the reactance used to determine the
current during the first cycle after the occurance of the
fault. In about 0.1 second this reactance increases to the
level known as Transient Reactance usually denoted as X'd,
and after 0.5 to 2 seconds it increases to the leven known
as Synchronous Reactance and denoted as Xd, and this
determines the fault current after a steady condition is
reached.
| Is This Answer Correct ? | 205 Yes | 27 No |
Answer / babak turkan
subtransient reactance in percent normally for induction motors is 16.7 5
| Is This Answer Correct ? | 19 Yes | 29 No |
i asked a funny question in Electrical ohms law V=IR in const temp voltage is directly proportional to current Power p=VI cos@ in that formula Voltage is indirectly proportional to current Try to give me the fact what is happening in Electrical.. contact Thanigai_1984@yahoo.co.in
What will happen if DC supply is given on the primary of a transformer?
what is the signification of trivector meter? why its name is trivector meter ?
How many 2 ton window A/c can runs on a 125 KVA generator?
In a synchronous motor. if start is running at high speed. What will be the starting torque : Higher Lower Zero
What is master trip relay? How does it work?
How much of the total hydro power potential has been exploited so far in india?
What is meant by a stray loss of a induction motor??? What is the equation to find it
diffrence between windings of high tension side and low tension side of transformer
I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current 36 A,but wenn i put load after 2 hours the current increase more than 156 A. Can anybode tell me waht is the Problem?
i will applied in 1U-1W on 440 volt primary delta side. what is the result of magtic balance test
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)