Answer / satya dev
For Alternator..... Over Voltage & Under Voltage Relay,
Over current & Earth fault relay but all these are not
directlay connected to alternator, It is connected to the
ACB of alternator to safe the Same during faults.
For Transformer...... Buckholz Relay, Winding temperature
Indication(Alarm & tripping system) Oil temp. Indcation etc.
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / taju
For Alternator- Under/over voltage protection,Reverse
power,under/over frequency,ground fault protection,
For TXR-Buckholz rely,winding temperatur,Oil
temperature,ground fault protection.
| Is This Answer Correct ? | 1 Yes | 0 No |
what are the duty ratings in DG sets?
hi, in the event earth grounding is not available in a project, is there any other way to make the elcb work? fyi, i have an instant water heater (6.5kw) installed, however if there is grounding in the heating element inside the heater assembly, i will get grounded. thank you in advance to those who will answer my question.
There are 2 Flip_Flop with logic between them. Given Clock to Q delay, logic prop. delay, set up and hold times specify maximum clock frequency of system. What happens if second output fed back to first input. Any changes? What happens with timing if second output is fed back to logic between the flops? Good Luck!
On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?
6 Answers RR, TNEB Tamil Nadu Electricity Board,
what is the difference between LATCH and FLIP FLOP
how much capacity(rating) of generator required to operate a load of 100kv.
various transmission tower like .,D tower ,K.C.O tower ,C.C.O tower,K.C.R tower ,C.C.R tower ,H.C.O tower in different tons.
What are the typical values of characteristic impedences of overhead line and underground cabel? Why there is so much variation?
For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating
What is the physical significance of phase.. i.e. what is exactly the meaning in layman's language.. 1 phase, 3 phase etc ???
why transformer are rated in KVA not in watt?
I have 200 KVA Isolation Transformer for UPS input side. & ups was having 48% load, suddenly got short what will be the reason.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)