what will happen if delta - star , 400V to 6.6KV step up
transformer neutral is not grounded, Neutral is not used
but transformer is provided with neutral.
Answers were Sorted based on User's Feedback
Answer / ahmad abu alrob
In princible two things may happen during fault condition
or unballance loading:
1- No earth fault protection will be operated.
2- Any Phase/ Neutral voltage could reach the value of
Phase/ Phase voltage in magnitude.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / raghavendran
If the system neutral is not grounded then during unbalanced
condition or during any faulty condition the excess current
will flow through the phases.During the condition of neutral
shifting the the current will flow into the system
itself.This will lead to damage to the equipment and the to
the personal working with the system.
Is This Answer Correct ? | 3 Yes | 2 No |
Why do we need interlocking in a HT metering or Ring main unit switchgear?
generator means
What is signal flow graph?
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
what is an unbalance in acircuit? in a three phase 3wire circuit how an unbalance will come? in a three phase four wire system how an un balance is coming?
What is meant by full pitched winding?
What is the Ideal Earth to Neutral Rating for Techonology Equipment like Routers, Switched, PABX, Computers etc etc?
What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?
What does negative slip of an induction motor signify?
We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
How can we calculate the capacity of the capacitor bank attached with the Main panel, when we know the capacity of the panel installed in KVA Rating?
Explain why the Voltage drop will happen in 3 Phase line?