Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What is the difference between an ELCB and a RCD?

Answer Posted / raghavendran r

ELCB stands for earth leakage CB.It trips any faulty circuit
by detecting the current flowing through the neutral.Under
normal condition, the intensity of current flowing through
the neutral must be the same as the current flowing through
phase to load then to neutral.If the intensity is not the
same then it means that the return current is deviating from
its actual path ie flowing through equipment body or if the
current is not returned properly.Now consider a case where
the return current is flowing through a operating persons
body(electrocution) after coming out from the load.
In this case, ELCB will not work because the return current
intensity flowing through the persons body is same.These
were the draw backs in older type of ELCB.
To over come this draw back RCD ie Residual Current
Detectors are used along with the ELCB which detects the
residual current deviation ie in case of any electrocution
also and then trips the Circuit.

To detect any

Is This Answer Correct ?    6 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses

1875


List the disadvantages of constant k filters?

1670


what's prime importance of protection in electrical system.if protection system don't work properly what can happen in electrical system?

1919


what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?

2035


dear sir, i completed diploma in electrical in 2005, how i can get electrical supervisor liance in mumbai

1968


how does ELR works? explain

2692


What are the effects of adding a zero to a system?

1301


What is the significance of integral controller and derivative controller in a pid controller?

1175


How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?

1947


working function importance of mdc meter

2168


Which device of PlC does share load between DG sets when DG are running in perallel?

2075


What are Contactors? How they works and what its highest rating?

2146


What does the term power factor shows?

1127


what is the minimum winding resistance of 30hp compressor, to run or to switch on

1876


What is distance between electrical panel to land ?

1543