what is the formula for calculating milliampere at different
pressure points for eg 4-20 ma = 3-15 psi but if i have to
check the ma at 4.6 ma?
Answers were Sorted based on User's Feedback
Answer / lalchhotex
as per as nick formula it is not fullfill anoter range like
as 0-100 for level, 0-14 for PH
formula is
16*(unknow value-Low end of rang)
mA O/P = 4+ ---------------------------------
transmitter span
Suppose range is 3-15 PSI according to question what is the
psi for 4.6 mA
by the formula
4.6-4 =16*(unknow value-3PSI)
----------------------
12 PSI
0.6*12PSI
--------- = (unknow value-3PSI)
16
7.2 psi
------- = (unknow value-3PSI)
16
0.45 psi = (unknow value-3PSI)
0.45psi+3psi = unknow value psi
3.45 PSI = unknow value psi answer
Is This Answer Correct ? | 23 Yes | 2 No |
Answer / gunasekaran
4~20mA=3~15psi
4.6mA=?psi
psi =(mA -mA Zero)/(mA Span)×Range Span+Range Zero
4.6-4
psi = ------ x 12+3
16
0.6
psi = ---- x 12+3
16
psi = 0.0375 x 12+3
psi = 3.45
4.6mA = 3.45psi
Is This Answer Correct ? | 19 Yes | 4 No |
Answer / abdulbasit137@hotmail.com
this is the one of the best formula for this situation
measuring value (1) - low ranmeasge value (1)/span
=
measuring value (2) - low range value (2)/span
u know span high value - low value 4 to 20 span is =16
3 to 15 span is = 12
simple
mv1 - lrv1 = mv2 - lrv2
span span
4.6-4/16= ?-3/12 = 4.3psi ans
Is This Answer Correct ? | 1 Yes | 13 No |
What is standard procedure of manual mapping in Radar type level transmitter?
what is the reset offset and control system in instrumentation
In close vessel/ drum why we use d.p. transmitter of -ve range i.e. (-)500 to 0 mmwc.
what is span adjusment of transmitter? what is the function of positioner/
What is the difference between ROM & RAM .
what is the difference b/w normal thermocouple and skin type thermocouple?
When we will do simulation for I/P?IF WE DO SIMULATION through which way either series or parallel?
which is the best type to measure level of a Tank(water). Displacer or Differential Pressure method?
in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com
hello friends, can you please send me the model paper or question paper to be prepared for hpcl examinations????????? You can mail me at rahim_here@yahoo.com waiting for your reply........... help me .. plz.....
what is sliding spool valves?
i have a dp tx range is 5000mmwc. in which calibration i use in a open tank.1.5*3.5*2.5 mtr.for level msmnt. what is the calculation.