Answer / deepak prabhu
5 Hp motor usually comes in 3 ph only.and DOL starter of 3 phase is also available. Cable size doesn't depends on KVA of generators. In 3ph, 5Hp=3.7KW. =11A. By cosidering factor of safety we can use 4.0 sq mm copper cable.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mohammad farman khan-abu dhabi
5HP Motor are use as single phase on D.O.L or Star/Delta
connection as 3 phase. If you use single phase then total
load is 3.7kw so we can use 6mm sq cable .if you use in y/D
connection the required to use 4cx6 sq mm cable.
| Is This Answer Correct ? | 3 Yes | 2 No |
What is the magnetic field (coil DC ) of Turbo Expander?
What is resolver and glass scale in CNC how they work?
if 20 hp motor starts directly stars and contenious run . what will be the effect.
11 Answers HP, Ohsung Electronics,
wat do knw aboot circuit breakers ?
Explain with example of functional requirements of protection relay in terms reliability, selectivity, sensitivity
what is Princepale of Transformer Taps.
why servomotor motor? where i apply for best output?
difference b/w series¶llel
What is the temperature PROFILE OF A FLUID W. R. T. Distance from a sphere to which it is IN CONTACT which is at constant temp.?
Why transformer is not rotating?
why DG neutral is earth?
Write a note on Treatment for electric shock.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)