How to size the Neutral grounding resistor?
Answer / nagarajan
For example 20/25MVA Power Trans -132/6.9kv
1. FLC of Secondary=2092A
2.Phase to Phase Voltage for Secondary=6.9/1.732=3.98Kv
3.NGR =3980/2092=V/I=1.90Ohms for 30sec
It is only for power transformer.