How to size the Neutral grounding resistor?
Answer / nagarajan
For example 20/25MVA Power Trans -132/6.9kv
1. FLC of Secondary=2092A
2.Phase to Phase Voltage for Secondary=6.9/1.732=3.98Kv
3.NGR =3980/2092=V/I=1.90Ohms for 30sec
It is only for power transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
3 phase supply is there Total kw 100 howmuch cable put the load
What should be cable size for 75KVA 380/220 3ph transformer
why transformer rated in KVA not in KW ? we know that W= v*i
What is the Maximum Power generation capacity of a Synchronus Machine ??
how to reduce humming noise in transformer?
any one have papers of hpcl or sailof ELECTRICAL ENGG.
what is the role of transistor in Circuit?
What is PTZ Camera???
3 Answers Cherrytec, CSC, Honeywell, Zicom,
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
generally rectifying of ac tells. ac signel appear at phase and neutral with respect to frequency by -veand +cycles. but we doesn't experience shock with neutral in house hold ac??????.
what is LA CT PT panel?
3 Answers Dwarikesh Sugar Industries, NTPC,
what is earth resistance? how to measured? and give values at power station and mcc area?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)