The motor is running due to the non operation of the thermal
over load relay. The motor will keep on running till the
winding temperature increases the designed limit, finally
the motor will burn under the winding short circuit
condition causing production loss & down time .
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / rajesh
Ans #1 is partly correct, but probably that is not the
intended answer. Rating of a motor is decided depending on
the ambient temperature. When you say that the rated
current is 38 Amps, what you mean is it can take a
continuous current of 38 Amps at the design ambient
temperature (say 40 degree C). During winter, the ambient
temperature may be 10 deg. At that ambient, it can take a
much higher current. (You can also give extra cooling of
the motor winding by providing an external ventilation
fan).
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sathiarajan
The motor is over loaded. It can work under over load for a
short time period.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sam
ya after the winding overheats it will damage the motor,
the check O/L relay setting and its functioning we had the
same problem.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / hameed
maybe there is a problem in load which this motor run it &I
wender if you cheak all the phases
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the voltages using in movie theaters??? why ??why not other??
1)How much current can a 3-1/2 core 100 mm wire carry? 2)What are the special cables required for explosion proof wiring? 3)In case you do not have coal and salt for earthing, how can you achieve good temporary earthing? 4)One horse power single phase motor is more likely to get hot than a one horse power 3 phase motor. Is it true or false, if true why? 5)What are the different types of soft starters for large motors?please explain?
Why we are using LA Rating 10kA in 66 kv substation
Why Neutral Earthing pits and body earthing is interconnected
can any one explain me the where is the use of plc and scada
why neutral and body earthing of transformers kept separated? what is distance between two is required as per is?
What sort of protection scheme do you suggest for the protection of a 10 HP motor?
What is differnce b/w tie breaker and bus coupler?
At what condition differential relay will act in transformer and ht motor?
onan full form
why the current leads voltage in the case of a capasitor
can a 50 Hz transformer work satisfactorily if placed under 60 Hz,what are the prices and losses that will arise
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)