can any one pl explain me in brief that how we select the
leakage classification in valve,means for liquid or gas
there is any standard for selecting leakage classification
or its depend upon valve size or any any other parameter.
Answers were Sorted based on User's Feedback
I cannot remember to much about this but I remember that the
leakage rate is dependent on the valve classification. a
Class 6 valve is a tight shutoff valve with not leakage
tolerance at all. a Class 5 is classified as a modulating
valve and have a tolerances of a small amount of droplets
per minute and so on. The lower the class valve the higher
the acceptable leakage rate. This leakage rate is tested in
a valve shop either by the manufacturer or on your own site
if you have the right equipment to do it with.
We normally had it done by our valve shop after we send a
valve to them for a complete overhaul. Once the control
valve have repaired and overhauled the valve, we had to do
the final testing and acceptance with them. They would
supply us with the specs on the valve so that we can see
what class valve it was and what the acceptable leakage
tolerance was. After this we would witness the testing of
the valve and sign a acceptance certificate.
I suggest you get hold of your valve shop or the original
manufacturer to supply you with a list of the
classifications of the valves you are currently using or
want to use as well as the various acceptable leakage rate
for each class.
Good luck
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / trupti
Class VI for Gas service as gas requires tight shutoff &
class I , II, III, IV, V for liquid service as per process
requirement shutoff
Is This Answer Correct ? | 2 Yes | 1 No |
CLASS 2............ 0.5 % OF CV..........MEDIA AIR
CLASS 3............ 0.1 % OF CV..........MEDIA AIR
CLASS 4............ 0.01 % OF CV..........MEDIA AIR
CLASS 5............ 0.0005 ML/MIN.........MEDIA WATER
CLASS 6............ 1 BUBBLE/MINIT.......MEDIA WATER
IN CLASS 6 IT WILL CHANGE DEPENDING ON THE SIZE
Is This Answer Correct ? | 0 Yes | 0 No |
why magnetic flow meter is not used in thermel power plant operation
How to gennerate earth leakage monitoring alarm for solenoid valves in control system?
What are primary elements of measuring pressure?
basic connection and principle of axial shift sensor n differential sensors in tubine describes n draw......
What is two wire system and how it work
I have transmitter of range -20 to -5 kpa.if it is possible to zero trim with atmospheric pressure,means HP and lp having no pressure...what will get after zero trim and it is the right way.....plz give me reply ....
PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..
how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)
What is expansion of SMART Instruments? And What is it?
Why thermo wells are used?
The wire is disconnected from the temperature sending unit (magnetic gauge). A voltmeter connected to the wire reads 0v. What does this indicate?
How to check electrical health of Vibration probe?