1)we r having one problem .one dry type
transformer(6.6KV/433V)is taking high magnetizing current on
delta connected HV side of "U" phase when compared to other
two phases.could any body tell the reason why it is happening?
2)why CT secondary side protection core has got higher
winding resistance when compared to that of metering core of
same CT?
Answers were Sorted based on User's Feedback
Answer / tanvir s.
Answerin ur 2nd query:
As we kno the flow of current is inversely proportional to the the resistance. Hence a lower resistance winding on the metering core of the CT would ensure a sensitive/accurate current(ampere) reading. Following the same principle the protection core has high resistance to limit the flow of over current and step it down to the calibration of the metering side.
Pls feel free to correct me if i am wrong or not clear
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mohamed
1.Check for no of turns ratio
2.check for phase angle difference
Sec side of CT always handle more current comparing to primary side
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the maintain in ACB,VCB,MCB,MCCB breakers?
Assuming that a dedicated neutral earthing transformer is provided for each GT generator, when the two generators are running in parallel, has consideration been given that the earth fault current from one generator stator winding be split between the two neutral earthing transformers? If so, what adverse impact will this have on the operation of the 59N and 27TN devices?
Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem
For a CT the number of turns in the primary winding is.........
1.what is surge 2.what is lightning 3.what is switching 4.difference between surge,lightning,switching used in power system 4.definition of surgearrestor,lightningarrestor 5.adv and disadv of surgearrestor,lightningarrestor 6.uses and purpose of surgearrestorand lightning arrestor 7.block dia of surge arrestor 8.blockdiagram of lightning arrestor 9.operation and working of surge arrestor and lightning arrestor 10.basic formula of surgearrestor and lightning arrestor 11.basic diagram of surge arrestor and lightning arrestor
1 Answers Crompton Greaves, Framo, L&T,
I have a 380 KVA DG set. How can i find out 1. My Fuel Consumption per hr ? 2. Electricity produced in 1 Hr. ? 3. If load varies then how does it affect fuel consumption & electricity produced ? Please HELP !!! Really need an answer.
what are the 6 terminals of the motor plss give me in details
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
how to calculate the capacitor rating for improving power factor
10 Answers L&T, Property Solutions, Synergy, TAFE,
How to choose size of the cable w.r.to current carrying capacity ...
Clearly Define Active,Reactive,Apparant power.Which applications used which power above metioned power?
what is reactive power (MVAR) and how it is control? how it is generate in powerplant?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)