Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


1)we r having one problem .one dry type
transformer(6.6KV/433V)is taking high magnetizing current on
delta connected HV side of "U" phase when compared to other
two phases.could any body tell the reason why it is happening?
2)why CT secondary side protection core has got higher
winding resistance when compared to that of metering core of
same CT?

Answers were Sorted based on User's Feedback



1)we r having one problem .one dry type transformer(6.6KV/433V)is taking high magnetizing current o..

Answer / tanvir s.

Answerin ur 2nd query:
As we kno the flow of current is inversely proportional to the the resistance. Hence a lower resistance winding on the metering core of the CT would ensure a sensitive/accurate current(ampere) reading. Following the same principle the protection core has high resistance to limit the flow of over current and step it down to the calibration of the metering side.
Pls feel free to correct me if i am wrong or not clear

Is This Answer Correct ?    2 Yes 1 No

1)we r having one problem .one dry type transformer(6.6KV/433V)is taking high magnetizing current o..

Answer / mohamed

1.Check for no of turns ratio
2.check for phase angle difference
Sec side of CT always handle more current comparing to primary side

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the maintain in ACB,VCB,MCB,MCCB breakers?

4 Answers   CTS,


Assuming that a dedicated neutral earthing transformer is provided for each GT generator, when the two generators are running in parallel, has consideration been given that the earth fault current from one generator stator winding be split between the two neutral earthing transformers? If so, what adverse impact will this have on the operation of the 59N and 27TN devices?

0 Answers   Quest,


Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem

3 Answers  


For a CT the number of turns in the primary winding is.........

5 Answers  


1.what is surge 2.what is lightning 3.what is switching 4.difference between surge,lightning,switching used in power system 4.definition of surgearrestor,lightningarrestor 5.adv and disadv of surgearrestor,lightningarrestor 6.uses and purpose of surgearrestorand lightning arrestor 7.block dia of surge arrestor 8.blockdiagram of lightning arrestor 9.operation and working of surge arrestor and lightning arrestor 10.basic formula of surgearrestor and lightning arrestor 11.basic diagram of surge arrestor and lightning arrestor

1 Answers   Crompton Greaves, Framo, L&T,


I have a 380 KVA DG set. How can i find out 1. My Fuel Consumption per hr ? 2. Electricity produced in 1 Hr. ? 3. If load varies then how does it affect fuel consumption & electricity produced ? Please HELP !!! Really need an answer.

0 Answers  


what are the 6 terminals of the motor plss give me in details

5 Answers   Siemens,


I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?

4 Answers  


how to calculate the capacitor rating for improving power factor

10 Answers   L&T, Property Solutions, Synergy, TAFE,


How to choose size of the cable w.r.to current carrying capacity ...

0 Answers   L&T, Saams,


Clearly Define Active,Reactive,Apparant power.Which applications used which power above metioned power?

9 Answers   Summit Power,


what is reactive power (MVAR) and how it is control? how it is generate in powerplant?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)