how to mention 5mw generator in kva ? gen voltage is 11kv
Answers were Sorted based on User's Feedback
Answer / rasesh
KVA MEANS KILLOVOLTAMPERE. IT IS AN ELECTRICAL UNIT TO
DEFINE THE RATING OF A MACHINE, KVA= KW/P.F.(COS @).
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / nawab ali
first in the question it is mentioned 5 mili watts(mw) ,if
it is so then the ans. will be= 0.005kva
and if you mean 5 MEGA WATT then the ans. willbe 5000 KW or
kva(Assuming that the power factor allmost unity. Always
keep in mind that alphabets used in electrical terms it has
some meanings so when ever asking any question use the
proper letters either capital or small.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / h r jadhav
power rating- 5000 kw
voltage -11000 volts
pf-0.86
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ramesh glv
watt means power
va means voltamp i.e voltage*current
VICOS@=P(POWER)
VI=P/COS@
| Is This Answer Correct ? | 0 Yes | 3 No |
What will be the sampling frequency that reveals the same sampled signal?
In wat way the power compensation takes place when a statcom is connected in a transmission line
I've descovered that when the earth wire in a domestic electrical installation is not connected back to the board (ground) a voltage of between 9-24v is is found to be present in the earth wire. When connected at the board there is no voltage - is this normal and why does it happen?
Which type of losses in transmission Line
What happens to an electric motor if it has poor or no ventilation. Will it burn out? If it will, how long it will run before it burn out?
how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.
What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.
what is tower earthing and what for it is required
minimu size and length of gi earth pipe
hoe to select the cable size in sq mm for certain load?
in indoor type circuit breakers why only the corner breaker trips specially during cold season. What is the reason.
an amazing situation was faced when an alive distribution panel with 415 volts and carrying almost 200Amps has become short and this metal cubical showing 220 volts against neutral and earth. to redress any confusion i checked the panel with help of single 200watts test lamp which also glowing with max.intensity b/w neutral & metal body of DB. amazing situation is that i hold the DB firmly more than once with necked foot means without insulated shoes but not received any electrical shock. whereas our all running gen sets neutral points also proper grounded and this short DB was completely earthed , this is beyond my understanding . any body explain how is it possible . our running gen set neutral also grounded firmly
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)