Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to mention 5mw generator in kva ? gen voltage is 11kv

Answers were Sorted based on User's Feedback



how to mention 5mw generator in kva ? gen voltage is 11kv..

Answer / rasesh

KVA MEANS KILLOVOLTAMPERE. IT IS AN ELECTRICAL UNIT TO
DEFINE THE RATING OF A MACHINE, KVA= KW/P.F.(COS @).

Is This Answer Correct ?    12 Yes 0 No

how to mention 5mw generator in kva ? gen voltage is 11kv..

Answer / nawab ali

first in the question it is mentioned 5 mili watts(mw) ,if
it is so then the ans. will be= 0.005kva

and if you mean 5 MEGA WATT then the ans. willbe 5000 KW or
kva(Assuming that the power factor allmost unity. Always
keep in mind that alphabets used in electrical terms it has
some meanings so when ever asking any question use the
proper letters either capital or small.

Is This Answer Correct ?    3 Yes 1 No

how to mention 5mw generator in kva ? gen voltage is 11kv..

Answer / khan

6250000VA 0r 6.25MVA

Is This Answer Correct ?    0 Yes 0 No

how to mention 5mw generator in kva ? gen voltage is 11kv..

Answer / h r jadhav

power rating- 5000 kw
voltage -11000 volts
pf-0.86

Is This Answer Correct ?    0 Yes 1 No

how to mention 5mw generator in kva ? gen voltage is 11kv..

Answer / rajesh kumar

5000 Kva

Is This Answer Correct ?    2 Yes 5 No

how to mention 5mw generator in kva ? gen voltage is 11kv..

Answer / ramesh glv

watt means power
va means voltamp i.e voltage*current
VICOS@=P(POWER)
VI=P/COS@

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

What will be the sampling frequency that reveals the same sampled signal?

1 Answers   CCP,


In wat way the power compensation takes place when a statcom is connected in a transmission line

1 Answers  


I've descovered that when the earth wire in a domestic electrical installation is not connected back to the board (ground) a voltage of between 9-24v is is found to be present in the earth wire. When connected at the board there is no voltage - is this normal and why does it happen?

3 Answers  


Which type of losses in transmission Line

2 Answers  


What happens to an electric motor if it has poor or no ventilation. Will it burn out? If it will, how long it will run before it burn out?

5 Answers   GMC,


how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.

0 Answers  


What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.

2 Answers   Siemens,


what is tower earthing and what for it is required

1 Answers  


minimu size and length of gi earth pipe

2 Answers  


hoe to select the cable size in sq mm for certain load?

5 Answers   TCS,


in indoor type circuit breakers why only the corner breaker trips specially during cold season. What is the reason.

0 Answers  


an amazing situation was faced when an alive distribution panel with 415 volts and carrying almost 200Amps has become short and this metal cubical showing 220 volts against neutral and earth. to redress any confusion i checked the panel with help of single 200watts test lamp which also glowing with max.intensity b/w neutral & metal body of DB. amazing situation is that i hold the DB firmly more than once with necked foot means without insulated shoes but not received any electrical shock. whereas our all running gen sets neutral points also proper grounded and this short DB was completely earthed , this is beyond my understanding . any body explain how is it possible . our running gen set neutral also grounded firmly

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)