Answer / vinaya
Calculation of voltage regulation is an important part of power system analysis.
ACSR, AAAC conductors of different sizes are available. Usage of a particular conductor depends on factors like voltage rating of the transmission line, power factor, total load, length of the line etc. For example following are the KW-KM values for 1% voltage drop at 60 deg C at P.F
1.00 - 41613; 0.9 - 25438; 0.8- 20966; 0.7- 17787 FOR acsr Coyote 26/2.54 + 7/1.91 conductor.
Generally the formula used for calculation of Regulation is
% regulation @ --- p.f = KW-KM X RC of conductor/P.F x D.F
Is This Answer Correct ? | 14 Yes | 6 No |
Answer / shiva
The above ans is general for calculating the regulation in
T.L. Due to capacitance effect in overhead transmission line
(short, medium, long) the regulation forumula is vaired.
Is This Answer Correct ? | 12 Yes | 8 No |
Answer / sks
Voltage Regulation is denoted in percentage.
Voltage regulation[%]= Vs-Vr*100
-----------
Vs
Vs = Voltage at Sending end.
Vr = Voltage at Recieving end.
different type of Conductor are useful as per current
carring capacity,resistance,length of
line,weatherproff,economics, market avilability, apearance
etc.
Is This Answer Correct ? | 14 Yes | 11 No |
How you will determine the volume of oil in a particular Distribution transformer.
What is called limb of a transformer?
how to convert the KVAR to microfarad??????????????????
What differance between Circuit brekar and Isolater?
What is the tolerence limit between neutral and earth in 230 V AC System?
Can the Neutral and Body Earthpits of a transformer conncted together by Earth strips under ground.
Why we are mention U1, V1, and W1 in primary side of transformer give technical reason
Why infinite busbar has zero resistance and high mechanical inertia?
why do we use LPF wattmeter not UPF in the experiment of no load and blocked rotor test of 3phase slipring induction motor?
when we connect the capacitor bank in series
The power showed in the name plate of the motor is input power or output power?? The power showed in the name plate is 18.5kw measured current is 34.5 amps. location is india. can i calculate the efficiency of the motor using this data??
What is meant rectifiers..