Answer / sudhakar g
According to Polycab standard the current carrying for 4C 50Sqmm STEEL WIRE ARMORED cable is 133A(ground) and 142A(air)
The formula for voltage drop is
Vd=(MV*Id*L)/1000
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / avd
Voltage drop in cable is a function of load current. It is
simply V=IRL. where V= voltage drop in cable, I= Load
current, R = Resistance/meter length, L= length of cable in
meters.
For maximum current carrying capacity of cable please see
menufacturers catalogue.
| Is This Answer Correct ? | 1 Yes | 0 No |
hi all my name is ganeshkumar from Hyderabad dee According to Poly cab standard the current carrying for 4C 50Sqmm STEEL WIRE ARMORED cable is 133A(ground) and 142A(air) ok use diversity factor demand foctor, all of i know use 80% load use in ex: 142*0.80=113 amps maximum load in air in ground 133*.80=106.4 amps maximum load
| Is This Answer Correct ? | 0 Yes | 0 No |
How to connect the chemical earthing and complete process tell me plz
What is the difference between AMF panel and DG Synchronization panel? please define the working of both the panels?
What is the major difference between P.T. & C.V.T ? Why CVT is used in HT Transmission line in place of P.T.?
Does the electricity supply authority send its customers power (kW) or voltape (V)? Asked by Ivan Muliro
I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.
What is the instrument to check the rotating diode fuse of alternator in running conditions?
WHAT IS THE USAGE OF Buckoltz relay IN POWER TRANSFORMER AND AND HOW ITS FUNCTIONS?
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
If I want to lift the water at a height 50m from ground level through two inch(diameter) metal pipe then what is the capacity of motor pump is required? is it possible in single phase supply or not?
In a HT switchboard where Nos. of Transformers are connected, how to decide Incoming cable size? Whether Cable should be rated for connected load or maximum demand?
what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?
please send me the L&T Emb. sys. placement papers and entire details of pattren
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)