Answer / anas
Eg3C x 35SQMM
Each core is 35SQMM (Core Red , Yellow , Blue)
To measure the conductor SQMM as per below
From BS 6360 Show that : 7/2.52mm
7/2.52mm is per below ;
Single wire diameter : 2.52mm (Based on BS 6360)
Number of Strand : 7wires (Each wire is 2.52mm)
Calculation
=(2.52mm)(2.52mm) x PI()/4 x Number of Wire (7)
= 34.9131 approximate 35SQMM
Is This Answer Correct ? | 47 Yes | 14 No |
Answer / p. h. godavary
Cable size (area of each core) is normally specified in square millimeters
(sq. mm). In this case it is 35 sq. mm. The cable size is always printed / marked on the cable itself by the manufacturer.
The conductor in each core of power cables is normally made of multi strand circular wires (Copper / Aluminum ).
To measure the size/area of the conductor, measure the diameter of a strand in a core and calculate its area. Multiply this area by number of strands in a core.
If the diameter of a strand in mm is D,
then its Area = [∏/4] [ DxD ] = [3.14/4 ] [DxD] Sq. mm.
Size of the cable (or) Cross sectional Area of a Core
= [Area of a strand x No. of strands in the core].
Is This Answer Correct ? | 33 Yes | 9 No |
Answer / p.h.godavary
In my answer (Answer #2), I have used the Phi symbol in the 'Area Formula'. But I find the same is appearing scrambled.
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / ali
you are measure the one conductor size 35 sqmm cable in
micro meter than you give a size in squre and multiple by
pae multiple by number of conductor dividing by number of
core,you are give the any cable size.
for example. i measure the 4 core * 300 sqmm cable size
(2.5)squre x pae x 61 /dividing by number of core 4
you have size the cable
Is This Answer Correct ? | 17 Yes | 21 No |
formula for calculation of switchgears(i.e. contactor, fuse, cb, relay etc.), if load current is given?
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
can any one provide me a connection wiring diagram for a DG set control panel along with BOM?
Any body can help me in getting LT panel test procedure.
Two electrically operated Vibro Motors are fixed in parallel direction in vibrating feeder. What is the direction of both Vibro Motors?
What is the acceptance value of leakage current in HI POT test
Apparent power is expressed as V * I(Conjugate). Why not in V * I ?
Diagram and details of polarity test for Current Transformer 11kv 400/200/100/1A
TNC switch is also available in 1NO+1NC. What does it mean ?
What are the testing to be done before the installation of 1000 KVA Transformer?
What is the effect of earth capacitance
difference between over current and over load protection?