How to calculate the actual 3phase power, if the load
current of each phase is not balanced
Answers were Sorted based on User's Feedback
Answer / shariff
It is recommended to use two watt mater method, then W1+W2 will give total power in all the 3 phase, this method can be used for this un-balanced load conditions.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / subbarao
Measure power in all the 3 phases separately and add them.
Is This Answer Correct ? | 1 Yes | 2 No |
why wire sizes are 3/29 or 7/29 and why not wire sizes are 2/29 or 6/29?
You are of electrical field and you are going for software? Why
What is best method of Calculating Short Circuit current in power system network.
WHY FLEXI LINKS ARE USED INBETWEEN GENERATOR TERMINAL OUTPUT & BUS DUCT CONDUCTOR.
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
what is the principle of operation of synchronous motor and generator? explain in detail.
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The slip when motor stalls is A 1 B 0 C 13.33% D 10.33%
why capacitor bank always connected in delta,why not in star to a system?
In case of a synchronous generator carbon brushes, some brushes expire before the others. Why is so? When all the brushes are installed at the same time, why don't thee expire at the same time?
My meter ratio is -/5 and ct ratio is 100/5 now what will be the multiplying factor and how ?
How many types of Differential protection are there? and what the special arrangement are made at the time of charging of a transformer on the Differential protection?