How much duration I can keep open the CT if it is under
loading condition(100 Amp load)?
Answers were Sorted based on User's Feedback
Answer / vijay
If CT IS OPEN UNDER LOADING CONDITION IT WILL BURST.
Is This Answer Correct ? | 6 Yes | 0 No |
when ct is open circuited there is more voltage at the open
ends. this voltage may dangerous, if touch it you feel
sevior shock. The ct turns will act secondary itself & the
voltage will be equal to
voltage at bus or cable X No.of turns of the ct
which leads to leathal voltage & the current path is open
thus circuit is not completed.We aRE using ct's for metering
& protection. The metering ct will not get saturarated after
its rated VA immidiately but the protective ct's are GET
saturarated after its rated VA.
Is This Answer Correct ? | 2 Yes | 0 No |
What is the difference between body earthing and neutral earthing?
when we connect the capacitor bank in series
If Neutral Grounding Resistor (GR) failed/shorted. Is it repairable.
why pull the single core cable?
what are the problems are there if power factor is leading
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
Is RTCC panel needs any control supply.
what is the main difference between power devices and signal devices
wat is the difference between rotor 1st stage fault and 2nd stage fault?
what is the difference between a hooter and a mcp
Upto what extent, the lagging power factor can be improved with the help of capacitors?
when we increased the current what do ?