HT motors are generally connected in star, what will be the
effect if we connect HT motor in Delta?
Answer Posted / iamdon
star coonection reduces the voltage appering across each
phase by root 3 times.It means we need to design the
insulation for lower voltage which is economical.Also due
to reduced voltage reduced currrent will flow through
winding so less loss so less heating of winding so less
cooling requirement for keep the temperature rise within
limit.
All these beauty will lost in delta connection.So delta is
not preferred..
Is This Answer Correct ? | 42 Yes | 3 No |
Post New Answer View All Answers
what kinds of Transformer oil grade is better for power transformer ?
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
Enlists the applications of sampled data systems?
can we use trip light with bus coupler?
how to generator maintenance (A Check, B check,Etc)
define reflection method?
Why is water motor not taking the pressure? what is the problem?
Different types of relay fault which phase sequence??
How we can calculate the Amps for the cable Ex:- For 1sqmm wire how many amps we can draw (calculation)
How will polarity test of Dy5 Transformer ?
Advantages of using generator circuit breaker (GCB) scheme in a power station ?
Why efficiency in thermal power plant is low?
what is meant by flywheel and its role in retardation test
What is the two pole structure?
Graphs of measuring power and speed on dc motor