what is the design voltage for 6.6KV 2000 KVAR HT capacitor?
Answer / altaf
It is 7.2kV. This is arrived by taking into account 10%
increase in supply voltage & rounded off. However this is
for installation where series reactors are not used. In
case a reactor is used (6% for HT) then the design voltage
is 6.6x1.1/(1-6/100) = 7.72kV. The design kVAr also needs
to be increased accordingly otherwise the output is reduced
and detuning percentage changes & detuning frequency
deviates.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the meaning of DY-11 Z-5%
what is emitter follower configuration? and what are it's features?
Can I use cable armour as a earth conductor? if not how many GI/CU wires I need to run along with cable?
wich type of cable is selected for wiring of 20hp motor?
Why converter duty transformer neutrals are not earthed...i am still not sure if this question is also correct...Please email at ranjan120482@gmail.com
IF we have 500kva transformer & know the current on HT & LT side, how can we consider for its breaker?
thyristor controlled APFC panel design parameter?
in transformer input is d.c signal which type of emf is induced
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system
what is acceptance test in electrical engineering.
If short circuit ratio is high is it bad or good for a machine then tell the reason...
WHAT IS ND RELAY AND HOW DOES IT WORK?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)