how we can calculate cable size of 230v,1 hp single phase
motor ? panel to motor distance is 25 meter
Answers were Sorted based on User's Feedback
Answer / vaibhav v t
You can use 3 core x 1.5 sqmm copper cable.Upto 5 hp three
phase or single phase your can use this cable.
| Is This Answer Correct ? | 15 Yes | 6 No |
Answer / abokamal
cable design.
first we have to choose CB.
(I)load=P/(V*PF)......... assume pf=0.8
(I)=746/(230*0.8)=4.1 Ampere
(I)cb=(I)load *s.f (FASETY FACTOR)=4.1*1.25=5.1 Ampere
(I)cable=(I)cb/D.F (DERATING FACTOR)=5.1/0.8=6.33 Ampere
from catalouge you can select the cable according to the
current.
you have to see (volt/ampere/meter) to see the voltage drop
limit which according to +-5%
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / vipin
kamal is right ,after deciding the load current you ll have to consider the starting condition....
as per the IEEE regulations you ll have to consider 3 to 4 times the rated current as the starting current...as the rated current is coming around 6 amperes you can select a CB of 20A DP or SP. A 4sqmm cable will be std for the 1 hp pump.. you will have to verify with your supply company rules for the size of cable to be used for the designed value of circuit breaker.
| Is This Answer Correct ? | 3 Yes | 2 No |
WHat is the requirement of installing FAST ACTING EARTH SWITCH in GIS and how is that integrated with protection system. How and when does it operate?
In what condition the HT fuse breakes?
Why we are putting off the APFC(automatic power factor control) panel while the generator is running?
After synchronization with grid how to maintain the power factor in lagging or in leading? if lead of lag what is the problem?
how to calculate multiplying factor with ct ratio 400/5
can you check the current and voltage of a 12 V battery by a digital multimeter in this fashion that apply the digital multimeter across the battery terminals directly ? say yes or no ... i sais yes ........... is this true or false ? plzz tell me and also explain ........ plzz thanks
i have applied for the post of RRB section engineering chennai board please send me previou papers and solved answer. my mail id jagarapusrinivas@gmail.com
What is Wlak Test in Fire Alarm System????
Hi Friend I am used multimeter to measure the voltage between R Phase(SS1) to R Phase(SS2). In SS1 is connected with UPS loads. But I am getting voltage between these 2 R Phases. Please give some idea friend
what is the difference between earth and neutral?
56 Answers Bhel, Emerson, HCL, JLL, L&T, Siemens, TVS,
ho can we calculate the conductor insulation value according to their ratings like voltage,current etc.how insulation value related with voltage,current and power of amachine
How to define Kirchhoff current law and voltage law along with simply examples.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)