how we can calculate cable size of 230v,1 hp single phase
motor ? panel to motor distance is 25 meter
Answers were Sorted based on User's Feedback
Answer / vaibhav v t
You can use 3 core x 1.5 sqmm copper cable.Upto 5 hp three
phase or single phase your can use this cable.
Is This Answer Correct ? | 15 Yes | 6 No |
Answer / abokamal
cable design.
first we have to choose CB.
(I)load=P/(V*PF)......... assume pf=0.8
(I)=746/(230*0.8)=4.1 Ampere
(I)cb=(I)load *s.f (FASETY FACTOR)=4.1*1.25=5.1 Ampere
(I)cable=(I)cb/D.F (DERATING FACTOR)=5.1/0.8=6.33 Ampere
from catalouge you can select the cable according to the
current.
you have to see (volt/ampere/meter) to see the voltage drop
limit which according to +-5%
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / vipin
kamal is right ,after deciding the load current you ll have to consider the starting condition....
as per the IEEE regulations you ll have to consider 3 to 4 times the rated current as the starting current...as the rated current is coming around 6 amperes you can select a CB of 20A DP or SP. A 4sqmm cable will be std for the 1 hp pump.. you will have to verify with your supply company rules for the size of cable to be used for the designed value of circuit breaker.
Is This Answer Correct ? | 3 Yes | 2 No |
what is the meaning of DSL
When we use PT in HT Panel why the ratio is 11Kv/√3/110v/√3 please explain briefly with suitable formula?
what is CT class? depending upon which it is classified?
Which types of following motors are most efficient?
what u meant by shock ? whether it depends on voltage or current
75kw drive operated motor current fluctuation from(85-130)ampere.current setting in drive is 130amp.sometimes motor trip when current limit cross 130amps.I change the drive. still current fluctuate between 80-130amps but in this time motor not trip,current setting in drive is 130amps.where is the problem?
What is a signal flow graph?
why should the primary of transformer be connected in delta in a heat run test?
How To increase Knowledge Of boliler regarding To Only Electrical Field..
What do you mean by linear and bilateral network?
20 Answers Automation, Disa, EGCB, Infosys, OPTCL, TICT,
what happen if one of 3-phase line has a much higher load when we are using delta to star transformer? how we can over-come from that?
why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer.
12 Answers ABB, Adani, Central Electricals, Electrical, HCL,