Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

how we can calculate cable size of 230v,1 hp single phase
motor ? panel to motor distance is 25 meter

Answer Posted / vipin

kamal is right ,after deciding the load current you ll have to consider the starting condition....
as per the IEEE regulations you ll have to consider 3 to 4 times the rated current as the starting current...as the rated current is coming around 6 amperes you can select a CB of 20A DP or SP. A 4sqmm cable will be std for the 1 hp pump.. you will have to verify with your supply company rules for the size of cable to be used for the designed value of circuit breaker.

Is This Answer Correct ?    3 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

how does a liquid starter reduce the starting currents?

2103


What is proportional controller?

1258


how we select ac fuse rating of an power inverter???

1849


what are the stresses in circuit breakers ?

1986


What is warm / cold start of HT motors. How many warm start & cold start are possible in a day?

2021


How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.

1698


Explain Energy and Power signals?

1720


why should the primary of transformer be connected in delta in a heat run test?

1950


For overhead protection we use which transformer?

2440


How to check the Bushings of the transformer?

1778


How to select HT/MV cable size ?

2431


How you calculate the repturing capacity of a HRC fuse

2588


Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA

1692


The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?

1586


what about SAP/MRP regarding manufacturing of electric motors and all drives?

1993